wendaiyu Member W Join Date Jun 2014 Location toronto Posts 87 Dec 23, 2015 #1 Hi, guys, how’s going? We want to build a connection between Logix5000 and Powerflex 70 via CnotrolNet. Could you tell us how to set up the node number on Powerflex 70? Because I cannot the instruction from Powerflex 70 user manual. Thanks a lot. Merry X-mas and Happy New Year!
Hi, guys, how’s going? We want to build a connection between Logix5000 and Powerflex 70 via CnotrolNet. Could you tell us how to set up the node number on Powerflex 70? Because I cannot the instruction from Powerflex 70 user manual. Thanks a lot. Merry X-mas and Happy New Year!
widelto Member Join Date Jul 2005 Location Barranquilla, Colombia Posts 3,392 Dec 23, 2015 #2 Look for a jumper that is used to enable drive. Go to the manual and for sure you will find it.
kamenges Member K Join Date Nov 2002 Location Green Bay, WI Posts 4,332 Dec 23, 2015 #3 If you don't already have this you will need a 20-COMM-C adapter installed in the drive. The ControlNet address is set on t his module. This manual will likely be of help: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/20comm-um003_-en-p.pdf Keith
If you don't already have this you will need a 20-COMM-C adapter installed in the drive. The ControlNet address is set on t his module. This manual will likely be of help: http://literature.rockwellautomation.com/idc/groups/literature/documents/um/20comm-um003_-en-p.pdf Keith