I'm trying to commission a DeviceNet network between a 1756-DNB scanner card and a Toyopuc DLNK-S2 DeviceNet card.

I see both the scanner and DLNK-S2 card in RSNetworx for DeviceNet, but I receive an E#77 fault (I/O size mismatch) when communications are trying to establish.

I configured the I/O parameters on the scanner card to send and receive 60 bytes each, and the DLNK-S2 is setup to send/receive 60 bytes each as well.

Anyone have any ideas on what I might be missing?
 
Thanks. Unfortunately, there is no EDS file for the Toyopuc card, so I/O area is empty. I created the I/O parameters to match the settings in the Toypuc PLC (see attached), but RSNetworx warns me that the connection sizes may not match (because the device in RSNetworx has no pre-configured I/O sizes).
 
I would try querying the I/O connection object in the Toyopuc. If they implemented it correctly, it will help you figure out the size of the Polled I/O connection.

The procedure for using RSNetworx and the "Class Instance Editor" to query the size of the Polled I/O Connection object in the slave device is described in RA Knowledgebase Article ID # 24919 (Access Level: Everyone).

I've seen lots of devices where they say "configure this in our software for X bytes" but then forget to say "plus two bytes for a header, if you've selected the optional DIP switch, and don't forget to cycle power".
 
Ken,

You hit the nail on the head. I used a previous post of yours (found through google) to query the device:

"
For a Polled I/O connection, the C/I/A values are Class 0x05 (Connection), Instance 0x02 (Polled), Attributes 7 and 8 (Produced and Consumed sizes)."

It turns out the Toyopuc card was sending 60 bytes, but only receiving 40 (still not sure why, since the card was set for 60/60).

Once I re-configured the polled I/O on the scanner, I was all set.

Thanks so much!

Regards,

Jason
 
Sweet ! Thanks for posting the followup.

The old "query the connection object" trick still works with Ethernet stuff these days; I helped a co-worker figure out a B&R X20 connection that way a couple of weeks ago.

On topics like this I've reached the point where Googling the problem results in my own solutions, so I think I'd better move on to another topic.
 

Similar Topics

Hi, I have a ControlLogix system with 1756-IF16 analogue inputs. I can't scale the inputs at the card as there is a requirement to facilitate...
Replies
11
Views
260
Hi all, installed on chassis A17 an A/I from Allen-Bradley , problem is what ever I do , all channels are sticked on value 39.9 and cannot change...
Replies
1
Views
141
I am using Allen Bradley PLC 1756-L81E and EIP module 1756-EN2TR for Ethernet/IP communication. My communication works fine but in Get-Attribute...
Replies
2
Views
202
Dear All: I have the flashing red light on the FDBK indicator. The manual said that it means: The axis servo loop error tolerance has been...
Replies
2
Views
635
Hi Guys, Here I have Started to work on some difficult task I hope I will get some solution here. I wanted to communicate ABB CI 840 IO Master...
Replies
2
Views
899
Back
Top Bottom