PV 600 to connect by RIO with SLC 5/04

BestTime

Member
Join Date
Jan 2016
Location
Ontario
Posts
89
Hi. I would like to communicate PanelView 600 by RIO (Remote I/O) with SLC 5/04.
On the laptop I use RSlogix500, communicating with RS232 (RSLinx DF1 driver).
The SLC504 L542 CPU is connected to the PanelView 600 with Belden cable.
I need to set up the pass through way, but dont know how.
Can someone help me?
Thanks
 
Last edited:
A SLC5/04 has a serial port ( 9-pin) and a DH+ port(s) only.

The 3 pin and 8-pin (round port) are DH+ only, they do NOT support RIO protocol.

As with your SLC5/03, your SLC5/04 will need a 1747-SN Remote I/O Scanner to connect to your RIO PanelView.

Sorry, but nice try.

See pdf.
 
Last edited:
I have the 1747-SDN C, scanner, but is the DeviceNet scanner.
So, you say I would need the Remote I/O scanner...
In the manual I was reading that the 504 CPU can take the RIO,
I thought that will be able connect using the DH+.
My other CPU is 503, that one can't use it for this.
 
Mickey, thank you for your support, I really appreciate it.
It looks like I need to either get another PanelView or a RIO scanner card.
Thanks again.
 
Just a quick thought: You may be able to get a 1747-SN off ebay for a pretty decent price. It may be cheaper to do it that way. IF you have the room in the chassis for the card.
 

Similar Topics

Hello PLCS.net! I am working with a EX600 Sen3/4 module from SMC. This is the documentation I am following...
Replies
12
Views
2,564
Hi. I am trying to connect PanelView 600, though RIO to the SLC500 DeviceNet card. I do not know if possible, but any help will bring me further...
Replies
13
Views
3,689
I would like to know to how connect my Dell Latitude D600 to a controlnet PLC 5. I need to know the cables neede.
Replies
2
Views
2,483
I have CPU313C-2DP , I want to connect it with ABB Softstart"PST142-600-70"by PROFIBUS network. I set ABB Softstart as following : Menu -->...
Replies
0
Views
1,967
I have CPU313C-2DP , I want to connect it with ABB Softstart"PST142-600-70"by PROFIBUS network. I set ABB Softstart as following : Menu -->...
Replies
0
Views
2,316
Back
Top Bottom