Gentlemen

I am having a difference of opinion with the mechanical guys (surprise). When a gaurd is opened, requiring a reset, does the resart of the machine require a separate action to restart?

Thanks
 
Totally agree, 20 year old machines, doing refits, and I am hearing "that is the way it has always been"

Just wish I could find a rule concerning this, good practice to give the operator a second to think yes I want to restart it.

Good practice doesnt cut it with these guys
 
Machine guarding is part of an emergency stop circuit.

If not, it should be....

To quote from this forum:

http://www.plctalk.net/qanda/showthread.php?t=82037


"6.2.5.2.2 Effects of emergency stop and reset commands
Once active operation of the emergency stop device has ceased following an emergency stop command,the effect of this command shall be sustained until the device is reset. This reset shall be possible only at
that location where the emergency stop command has been initiated. The reset of the command shall not restart the machinery but shall only permit restarting."

This excerpt is from CSA Z432-04, safeguarding of machinery. "
 
Machine guarding is part of an emergency stop circuit.

If not, it should be....

To quote from this forum:

http://www.plctalk.net/qanda/showthread.php?t=82037


"6.2.5.2.2 Effects of emergency stop and reset commands
Once active operation of the emergency stop device has ceased following an emergency stop command,the effect of this command shall be sustained until the device is reset. This reset shall be possible only at
that location where the emergency stop command has been initiated. The reset of the command shall not restart the machinery but shall only permit restarting."

This excerpt is from CSA Z432-04, safeguarding of machinery. "

Good and practical information but we do not necessarily follow the CSA directive here in the States.
The OP should have the US equivalent to be most effective at his location.

But then in his location I hear that pretty much anything goes.
 
Originally posted by timothymajka:

...I am hearing "that is the way it has always been"

That'll look good on somebody's tombstone.

Having an automatic cycle restart on a guard reset is probably not the best idea. However, only you or whoever at your site evaluates hazards can really make that determination based on the hazards involved.

Keith
 
I do automatic restart on the safety system, only if there is no chance of another person being exposed to the hazard. I always make the restart of the machine function manual.


ISO 13849-1:2006(E)
5.2.3 Start/restart function
The following applies in addition to the requirements of Table 8.
A restart shall take place automatically only if a hazardous situation cannot exist. In particular, for interlocking guards with a start function, ISO 12100-2:2003, 5.3.2.5, applies.
These requirements for start and restart shall also apply to machines which can be controlled remotely.

NOTE A sensor feedback signal to the control system can initiate an automatic restart.

EXAMPLE In automatic machine operations, sensor feedback signals to the control system are often used to control
the process flow. If a work piece has come out of position, the process flow is stopped. If the monitoring of the interlocked safeguard is not superior to the automatic process control, there could be a danger of restarting the machine while the operator readjusts the work piece. Therefore the remotely controlled restart ought not to be allowed until the safeguard is closed again and the maintainer has left the hazardous area. The contribution of prevention of unexpected start-up provided by the control system is dependant on the result of the risk assessment.
 
OP, I feel your pain... Once upon a time I worked at a plant that had a controls team and an Electrical Lead. Back in those days an Engineer could just ask his boss. Seems like the days are gone when you can just ask someone who knows as much or more about controls than the engineer on the project.... Or are we just working at the wrong places?
 

Similar Topics

Hello again..trying something on an existing poorly written program and just wanted to double check something system is an A-B MicroLogix 1200 In...
Replies
5
Views
165
Good morning! Let me start by saying, I am still learning about this type of HMI programming. I recently watched a video about recipes and how it...
Replies
0
Views
68
I have some logic that I have written within a 5380 series controller that tracks the time an event is started, while the event is running an RTO...
Replies
2
Views
91
I have an HMI 2711R - T4T Series B, and I want to know which PLCs, besides Micro 820, can communicate with it.
Replies
2
Views
80
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
79
Back
Top Bottom