AB L36ERM Connection to Vacon via Ethernet/IP

Johnny Boy

Member
Join Date
May 2013
Location
WA
Posts
10
Hi Guys,

I have been asked to integrate a machine with a vacon vsd into a control network. It is a vacon NX and the option board is an OPTCI.This board is a MODBUS/TCP option board. The machine builder says it can communicate via Ethernet Ip.The manual for the option card refers to Ethernet ip as well as Modbus set up. I have tried to set it up in the I/O tree in RSlogix 5000 V20.1 as a generic Ethernet Module but I can not set the input and output assembly in the manual it shows as not used. The manual is very vague and when I look on the net for vacon I keep getting redirected to the Danfoss web site. Do I need to use a pro soft MV169E-MBTP?

Thanks in advance for any feed back!:site:
 
MV169E-MBTP has only serial ports. For Modbus TCP/IP application you have MVI69-MNET:

http://www.prosoft-technology.com/P...-TCP-IP-Communication-Module-for-CompactLogix

http://www.prosoft-technology.com/c...55/version/15/file/MVI69_MNET_User_Manual.pdf

Prosoft modules are integrated in the Logix I/O tree using a generic module. Also Prosoft provides the logic to run the communications. You only need to design your communications table (registers to be read/writen on your remote I/O).

I found the manual for OPTCI here:

http://www.vacon.com/ImageVaultFile...OPTCI-Modbus-TCP-Board-User-Manual-DPD009.PDF

I think if you know about modbus specifications, you have all the tools you need to start the integration.

By the way, I think you would must consider adding a hardwired stop signal from the PLC to the VSD.
 
option card refers to Ethernet ip as well as Modbus set up
Can you point where does it say that it supports Ethernet/IP protocol?

It looks like this car supports Modbus TCP only.
You may be able to use Modbus TCP Sample code via Sockets or Prosoft Modbus TCP card.
 

Similar Topics

Hi Guys, I want to connect my 1769-L36ERM to a different network domain, is it possible to do it using only the dual ports in the Controller? Or...
Replies
3
Views
210
Hi there, Just a quick question. I have CompactLogix controller L36ERM that gives me energy storage fault. Controller is running fine. However...
Replies
6
Views
444
Does anyone know how many connections are available on a 1769-L36ERM Compactlogix? I have one that is connected to an Ignition SCADA system that...
Replies
4
Views
820
Dear all, Im using Allen Bradley Compact Logix L36ERM as a PLC. and facing a problem where I need to create a FIFO buffer that fills an...
Replies
5
Views
1,650
I cant get my L36ERM to recognize any expansion I/O (1769). Is this a processor revision issue. I had to update firmware on the processor ,when it...
Replies
14
Views
3,767
Back
Top Bottom