Hi Guys i am having some serious problems:
Attached is a fault table from the one PLC which I took, what basically is happening is the Ethernet Module does into a halting state and the “Log Empty” LED is not illuminated anymore,
The PLC shows no faults or warnings and the PLC is still running, only the Ethernet modules goes into this halt, when this happens I can’t ping or connect to the PLC we have to physically go press the reset button on the Ethernet module to get it back online.
We are inspecting the network infrastructure , thus far we have found anything, there is a fiber cable which was opened in a trench, we tested it and found no problem, the comms to the switch on the other end of it also shows no problems.
Also said PLC04 has inter PLC communication to PLC01,PLC02,PLC03 and PLC05, Mill 2 PLC does not have any interplc comms and is only connected to the main SCADA which runs on a different network.
Is there a way via the PLC software which we can reset the Ethernet module without needing to run out everytime or is there a way to disable the halting state so atleast production can continue while we are still looking for the fault?
PLC is the GE IC695CHS012 en the Ethernet card is a IC695ETM001
Attached is a fault table from the one PLC which I took, what basically is happening is the Ethernet Module does into a halting state and the “Log Empty” LED is not illuminated anymore,
The PLC shows no faults or warnings and the PLC is still running, only the Ethernet modules goes into this halt, when this happens I can’t ping or connect to the PLC we have to physically go press the reset button on the Ethernet module to get it back online.
We are inspecting the network infrastructure , thus far we have found anything, there is a fiber cable which was opened in a trench, we tested it and found no problem, the comms to the switch on the other end of it also shows no problems.
Also said PLC04 has inter PLC communication to PLC01,PLC02,PLC03 and PLC05, Mill 2 PLC does not have any interplc comms and is only connected to the main SCADA which runs on a different network.
Is there a way via the PLC software which we can reset the Ethernet module without needing to run out everytime or is there a way to disable the halting state so atleast production can continue while we are still looking for the fault?
PLC is the GE IC695CHS012 en the Ethernet card is a IC695ETM001