AB Micrologix 1000
24VDC System

I tried searching and was unable to find an answer, so I apologize ahead of time if this is a total beginner question that everyone should know.

I wrote a program to accumulate pallets on 6 conveyors of various lengths each (13', 9', 4x4' pieces). I am about to build the control box but I was curious if I should wire indicator lights on my panel directly to the same output that controls the contactors or if I should include a separate rung that if the motor is active OTE to a status light? I'm not sure if I should power multiple devices from a single output even if within voltage capacity.

----]XIC.M1[------]OTE.M1.LIGHT[--


Part of me likes the fail safe idea if the motor relay is getting power I want the status light to have power as well without programming error, hardware failure, etc...

Thanks,
Ben
 
Ben,
Wiring to the same PLC output for a status light is fine. Just be cautious of the current draw of your relay contactor and the status light do not exceed what the PLC can output.
If you want a super robust status light, use an extra-pole contactor and use the extra pole to power the light. That way the light shows the exact status of the contactor even if the PLC has failed to control it.

Tim
 
Thanks for the quick reply.

That's a great suggestion. I have already purchased the equipment for this installation but will definitely consider that in the future.

Thanks again!
 

Similar Topics

Hello everyone, This is my first post in the forum, although I have been here more times that I can count for various questions I have had from...
Replies
1
Views
1,214
I am working with a remote rack with a 1771-ASB adapter, and inside Logix 5000 I am trying to find where it displays the status of each of the...
Replies
8
Views
117
Hello, I'm working with Studio 5000 and ME Station, and I'm trying to find a way to detect if the PC with the HMI is shut down or not. I've tried...
Replies
5
Views
138
Hi I have a ifix 5.5 application where the operator opens a valve by clicking on a screen object. I can trace from object to data base that it is...
Replies
2
Views
64
Hi all. I have 1793-IE4 (4)analog inputs modules in a 1794-ADN IOFlex DeviceNet Rack. I cannot find if I can I have access to individual channel...
Replies
1
Views
70
Back
Top Bottom