Hi I have a heat exchanger supplied by steam at 6.5 bar
The steam goes into a automated ball valve and then a modulating valve, and into the HX. The condense line has a trap and a non return valve which goes into the condense header
The control scheme is to open the ball valve when the temperature is below the setpoint and close it when it is at setpoint +5
The modulating valve has a PID loop which is limited to 10% manual mode for 2 minutes before the PID kicks into auto and the valve opens to approx 80% and settles to around 25% and maintains the setpoint
The issue is that the ball valve has stainles steel ball and steam eats it in 8-10 weeks and the modulating valve lets by
On start up the steam hammers for for 2 mins at 10% but i am being told that increasing the 10% opeing may damage the piepework etc
Any suggestions welcome .. I am thinking of a automated condense drain line
system where the plant steam comes from a header and is reduced to 6.5 bar. This 6.5 Baris 6.5 bar. This is
The steam goes into a automated ball valve and then a modulating valve, and into the HX. The condense line has a trap and a non return valve which goes into the condense header
The control scheme is to open the ball valve when the temperature is below the setpoint and close it when it is at setpoint +5
The modulating valve has a PID loop which is limited to 10% manual mode for 2 minutes before the PID kicks into auto and the valve opens to approx 80% and settles to around 25% and maintains the setpoint
The issue is that the ball valve has stainles steel ball and steam eats it in 8-10 weeks and the modulating valve lets by
On start up the steam hammers for for 2 mins at 10% but i am being told that increasing the 10% opeing may damage the piepework etc
Any suggestions welcome .. I am thinking of a automated condense drain line
system where the plant steam comes from a header and is reduced to 6.5 bar. This 6.5 Baris 6.5 bar. This is