kamenges
Member
My turn to post a non-plc related question. Believe it or not, it's drive related.
Most drive manufacturers specify the overload capacity of their drives in terms of percent of rated current for some time (150% for 1 minute, for example). However, what does that mean in terms of torque when using field oriented control?
For the purposes of this discussion assume a perfectly matched drive/motor pair operating in field oriented control (or some other 'vector' equivalent). With a typical induction motor in the 5HP - 30HP range roughly half the current goes to develop the rotor field and the other half generates torque. If you assume the rotor field is controlled at it's optimum point (near saturation) this MIGHT infer that all the additional current goes to producing torque. Since rated torque is developed using 50% of the drives rated current this would mean that a drive developing 150% rated current will develop 200% rated torque in the motor connected to it.
Am I all wet with this or is this correct? The question comes from calculating how quickly I can decelerate a load with a motor given the drives overcurrent rating.
Thanks,
Keith
Most drive manufacturers specify the overload capacity of their drives in terms of percent of rated current for some time (150% for 1 minute, for example). However, what does that mean in terms of torque when using field oriented control?
For the purposes of this discussion assume a perfectly matched drive/motor pair operating in field oriented control (or some other 'vector' equivalent). With a typical induction motor in the 5HP - 30HP range roughly half the current goes to develop the rotor field and the other half generates torque. If you assume the rotor field is controlled at it's optimum point (near saturation) this MIGHT infer that all the additional current goes to producing torque. Since rated torque is developed using 50% of the drives rated current this would mean that a drive developing 150% rated current will develop 200% rated torque in the motor connected to it.
Am I all wet with this or is this correct? The question comes from calculating how quickly I can decelerate a load with a motor given the drives overcurrent rating.
Thanks,
Keith