As you will soon be able to tell from my question, I am not a Simens expert!

I want to take PIW300 (from a connected RTD) and divide it by 100 and put the result in a real.

I'm trying to figure out what conversion instructions I need to use. Step 7 keeps complaining of a type conflict.

Thanks!
 
I can follow your statement list with info from the help file... :)

But, if I may indulge you, how would you do it in ladder? A contractor used FC105 scale block and now all the RTDs read wrong. So I am just trying to replace a single network within the ladder.
 
Wait, maybe I figured it out. Didn't realize I had to divide then convert to double then to real. I'll try it...
 
You can both use ladder, stl, and fbd in a single block. But only 1 type per network.

its probably easier to do in STl as you wont need temps for the in-between values.
 
Last edited:
All the RTD's are reading wrong you said, are the min/max values set correct on the scaling blocks?

RTD's are showed with one or two decimals on integer variable. FC105 scaling block don't work, because it assumes that raw data is between 0-27648 (or -27648 and 27648)
 
RTD's are showed with one or two decimals on integer variable. FC105 scaling block don't work, because it assumes that raw data is between 0-27648 (or -27648 and 27648)

My bad, i'm used to our software generator so we hardly have to do anything with analogue inputs. I was asuming that thermocouples also where. -27648<>27648
 
My bad, i'm used to our software generator so we hardly have to do anything with analogue inputs. I was asuming that thermocouples also where. -27648<>27648

Quick fix is FC105 block (bipolar setting) and scaling to -276.48 to 276.48, if temp range is enought for application (I think that 1 or 2 decimals for input is selectable from RTD card's configuration so range -2764.8 to 2764.8 is also possible?)

But converting int -> dint -> real -> divide with 100 gives same result and full temp range ;)
 
Last edited:
Quick fix is FC105 block (bipolar setting) and scaling to -276.48 to 276.48, if temp range is enought for application (I think that 1 or 2 decimals for input is selectable from RTD card's configuration so range -2764.8 to 2764.8 is also possible?)

But converting int -> dint -> real -> divide with 100 gives same result and full temp range ;)

Just now saw your response. I actually did both of those in my playing around today. I find all the type conversions a bit clunky as I'm used to A/B handling that automatically. But, I'm getting better with the Siemens stuff... just need more practice. :)

Though I still can't figure out why one of my RTD inputs is always at 32767 counts with no RTD connected. All the other (5) channels downscale except this one. It does read correctly when I hook up the RTD, though. After double-checking wiring, I've concluded it is in the card. I have another identical system that I'll try tomorrow and see if it behaves the same way.
 
Last edited:
check manual for the card, at least some Siemens RTD cards have wire break setting for channels.

"Wire break" diagnostics enabled, 32767 / 7fff = "Open circuit" diagnostics message
Wire break" diagnostics disabled, -32767/ 8000 (hex) ="Lower limit value undershot" diagnostics message
 
Last edited:

Similar Topics

Hi Siemens guys! I am experiencing SF fault on our S7-300 (6ES7 315-2AH14-0AB0) CPU from time to time. I've checked the diagnostic buffer and...
Replies
13
Views
164
Have a system that has been running for over a year and all of a sudden getting a ExcessiveVelocityFault on one of the drives when the MSO command...
Replies
2
Views
142
Hello PLCS.Net Forum, First time posting. Let's assume I am a novice. BASIC PROBLEM: My servo/linear piston is no longer zeroed to the...
Replies
9
Views
216
hi... i have an issue in s7 300 plc, while we run the machine(in idle there is no fault) , plc cpu goes in SF mode, after restart the power cycle...
Replies
2
Views
117
gents, I am trying to configure communication with EMERSON PK300 controller through port A1 using generic ethernet communication module . I could...
Replies
0
Views
93
Back
Top Bottom