Hi,

I have a system who is built up with 400H and Intouch HMI (two IO servers, two physical computers).
I have some problem with the redundancy, if I`m diconnect the ethernet cable on master CPU intouch switch over and start pooling data from the other CPU on the 400H system, but the challenge is if I set the CPU to stop then the intouch dont switch over...

Summary:
Intouch don`t detect that the CPU is in STOP...

Somebody have any articles etc, how to configurate Intouch the right way when its communite with a 400H system?
 
Somebody have any articles etc, how to configurate Intouch the right way when its communite with a 400H system?

Aside from asking why the CPU is being stopped...

You might be able to do this via some form of scripting on a data change event where you are monitoring some form of boolean tag as a heart beat. Something where InTouch sets a bit, but the PLC resets it. So if the PLC doesn't reset it after some period, trigger the script to manually changeover the IO server. Might take some magic to make it reliable, and no I don't have code examples but I've done similar IO server swaps via scripting, just not triggered by a CPU stop.
 
Aside from asking why the CPU is being stopped...

You might be able to do this via some form of scripting on a data change event where you are monitoring some form of boolean tag as a heart beat. Something where InTouch sets a bit, but the PLC resets it. So if the PLC doesn't reset it after some period, trigger the script to manually changeover the IO server. Might take some magic to make it reliable, and no I don't have code examples but I've done similar IO server swaps via scripting, just not triggered by a CPU stop.

Same reason as Siemens selling 400H :)
Critical system who must not go down...

So we simulate fault on the CPU by set the switch to stop.

Thank you for your feedback, I just wanted to make sure that Intouch dosent had any inbuild function for these against 400H,
before I start making my own script.

So I will make a script working like a roller counter, and if the counter stop then shall it switch.
What command / function shall be used in Intouch to switch I/O server?
 
Last edited:
What command / function shall be used in Intouch to switch I/O server?

IOForceFailover("AccessName")


Does the Siemens 400H have system bits? I know that the Modicon PLCs we use have a system bit that is set to "0" anytime the PLC is not in RUN.
 
Last edited:
IOForceFailover("AccessName")


Does the Siemens 400H have system bits? I know that the Modicon PLCs we use have a system bit that is set to "0" anytime the PLC is not in RUN.

You can read out the status of the H-system by reading out the relevant system status list (SSL). SSL id 0x71 should do the job.

You can read the data from the PLC program with SFC51, and from remote via standard S7 communication.

Only reading the status from the plc program is not enough, as if the CPU is in stop mode, also the SFC call is not processed.

Some time ago we have programmed such thing in WinCC where it was not neccessary to have a switch over in milliseconds. If you need this, WinCC has a special package for this (Redconnect).

We have programmed two things:
Read out the current master CPU from PLC program using SFC51, and in WinCC read out the status bits from both CPUs. If both CPU are in RUN, then by default connect to the current master CPU.
And second we have used a livebit counter. If one counter stops and the other is still running, then switch over to the other CPU.
 
Thank you all for your feedback, we are up and running with full redunc. now :)

Thank you.
 

Similar Topics

Hello All, For S7-400H system, can we make this redundant PLC (connected to one uplink switch) to communicate simultaneously with 3rd party HMI...
Replies
2
Views
1,464
I need help from anyone with access to run a test on a 414H, 416H or 417H PLC system. The purpose of the test is to measure the communication...
Replies
0
Views
1,305
Hi all, I'm strugglin with mtbf calculation for my system, that is a siemens sistem H with double central rack and double et200M redundant on...
Replies
0
Views
1,508
Morning All As part of a SCADA upgrade I have inherited a pair of S7-400H processors and some remote I/O. I have a backup of the Step 7 file and...
Replies
9
Views
2,869
Dear All, Some questions regarding Modbus communication to DCS. i have a program and communicating to DCS through DB401 for analogs and DB402 for...
Replies
0
Views
1,688
Back
Top Bottom