Hello, I have problem to make conection via RSLinx with Panel View 7 2711P.
I see him but as unrecognized device. Is there any option with EDS or something similar.
I need to conect that panel(2711P) with MicroLogix 1100 Series A.
Is that possible?
 
You title implies that you are trying to communicate with the PV using RSLogix 500. The PanelView Plus requires Factory Talk View.
 
You title implies that you are trying to communicate with the PV using RSLogix 500. The PanelView Plus requires Factory Talk View.
Yes, my mistake. I have Factory Talk but also there is "unrecognized devices".
When something similar happens on RSLogix 5000, i simply install EDS or AOP.
But here i dont know what to do.
How I can add that panel so RSLinx can recognize him?
 
I've not come across that problem so I'm not sure how to help. My guess is that the PV+ is newer than your version of RSLinx so I'm guessing you might need to update RSLinx
 
I'm not quite following what you are trying to do. RSLinx Classic is not used to do work with Panelview Plus 7.

Are you trying to transfer the runtime file over? If so, you use RSLinx Enterprise to set the path from the PV to PLC then use the Tranfer Utility to transfer the run-time file to the PV.
 
I'm not quite following what you are trying to do. RSLinx Classic is not used to do work with Panelview Plus 7.

Are you trying to transfer the runtime file over? If so, you use RSLinx Enterprise to set the path from the PV to PLC then use the Tranfer Utility to transfer the run-time file to the PV.

It turns that Panel isn't supported with version of my RSLogix 500, so I changed that Panel with older version of Panel.

So, on that way I solved the problem.
 
And thank you all for your valuable time and attention to the problem that was presented.

Pretty sure your input contributed to his ability to solve his problem

Just saying a simple "Thank you" is in order.
 
And thank you all for your valuable time and attention to the problem that was presented.

Pretty sure your input contributed to his ability to solve his problem

Just saying a simple "Thank you" is in order.

I am sorry, I am just in middle of project which should be done very quickly!
So I just forget to say thanks, because my mind is overheated :D
Now I apologize and I want to thanks to all :geek:

All of you help me a lot.

Thanks once again!(y)
 

Similar Topics

Hi Everyone, I am not proficient in RSLogix 500 so I have a question regarding the evaluation of N7:0 data as an input. So as I understand in...
Replies
1
Views
81
I have a little bit of experience with Allen-Bradley. I have a Micrologix 1500 (RSLogix 500) and a PanelView Plus 7 (FactoryTalk View Studio ME)...
Replies
3
Views
161
buen dia. tengo una falla al pasar los tags de mi plc SLC 5 0/4 a mi panel me aparece un error Problem writing value " " to item <tag name>...
Replies
1
Views
81
Will someone please convert this logic to pdf?
Replies
2
Views
127
Hello, Haven't been on in a while. I need to generate a bit level pdf of the I/O for RSLogix 500. I can generate a report but it just shows the...
Replies
1
Views
158
Back
Top Bottom