Good day,
Orifice details d=92.36mm, max flow rate =120m3/hr, max diff =0-100mm wg. And my dp cell is calibrated to 0-25kpa. Is this correct cos converting 100mm wg gives me 0.98pka
 
The DPs range of 0 - 25kPa is about 0 - 2550mm wg

You need a range of 0 to 100mm wg

The range of your differential pressure flow meter needs a turndown of 25:1; 2550/100 = ~ 25. Not all DPs can do that.

If the DP can be ranged to 0-1.0 kPa, then it should work.
 
Dan is absolutely correct. Most flow meter/DP transmitters have about a ten to one turn down.

Frankly I would just go ahead and buy a new transmitter. It will be less expensive in the long than all the screwing around you will have to do to get questionable results from the existing transmitter.
 
thnx dan and tom. the calibration and orifice details just dont make sense. thank you for clearing that up. cheers and god bless.
 

Similar Topics

Dear all, hope you are well, A friend ask my for he has an orifice is worked at hydrogen service with high flow after that he needs to use...
Replies
2
Views
1,311
What is the best program or excel sheet for orfice calculations to download it
Replies
5
Views
2,214
Hello, what is the equation to measure gas flow across an orifice plate? i have a customer who has an orifice plate, DP transmitter, pressure...
Replies
9
Views
4,740
Anyone ever use A dynamic orifice valve before? Its basically an orifice plate that is an iris that can change size...
Replies
3
Views
2,515
We are undertaking a job consisting of replacing a gas valve motor and air damper on a burner with a control valve for the gas and variable speed...
Replies
19
Views
7,820
Back
Top Bottom