Hello dear all ,
I have a big trouble in the plant since last October.
I had a motor + VFD (ABB ACS800 12 pulse) , 1200 kVA , 690V. Transformer is 31,5kV/0,7kV - 6 pulse from 2007. The system was running properly since that time. This is a fan application.
And some strange faults started at October 2015.
One Rectifier module were damaged. We changed the module with the spare one. Some days later , other rectifier module damaged. We changed also this one. You could see nothing damaged or burned.
Some days later , this time , one module of inverters had exploded. A serious damage , inside of the inverter was burned and IGBTs were damaged. We replaced with the spare module.
According to some measurements , THD voltage was %6 and THD current was %20.
Again , after some days , another inverter was exploded. Same situation , it was burned completely. We called the service and started to work together.
Some doubts about motor appeared. We changed the motor. We checked the cables from VFD to motor. We checked the grounding around the system and everything seemed O.K.
While service was here the explosions went on. I don't know how many explosions happened but they changed everything inside the VFD , including all modules , all cards , all control systems. But it exploded again.
We changed the VFD with another VFD (Siemens Sinamics G150 - 1500 kVA - 12 pulse) on November 2015. And it was running properly to February 2016.
On 20 Feb 2016 , circuit breaker was tripped ad MV side. We saw that one side of the rectifier and inverter were burned. Service came and they changed the rectifier power module. They changed the inverter module. By the way we changed the motors from transfo to VFD and from VFD the motor. System started again.
Yesterday night , other rectifier side exploded.
We are stuck. Anyone had some experience such a like that problem before ?