Hi guys,

I have two Modicon 984 connected via Modbus Plus. The first PLC has a BMOT card attached to it to control a linear slide.

I made some changes to the program off line and downloaded the code after clearing the PLC memory using the "Initialise Logic" command which wipes the memory completely.

I downloaded the code and restarted the PLC controller and my linear slide start acting funny. It's full stroke is 9" and normally homes in one continuous movement. However, it would start homing moving 1" at a time and then stop before moving another inch.

Eventually I disconnected the power to the CPU and when I powered it back up the 2nd time the linear actuator worked properly again.

This isn't the first time that this has occurred. We have 33 of these slides and they go funny the odd time that we download a program.

Has anybody any ideas what I might be doing wrong?

Thanks,

Colm
 
Sounds like a typicle, "we don't employ a recovery routine" type senario. When you make changes to a motion device, or the program that controls that motion, the encoder count is not updated. You should, as a method, incorporate a recovery or initialization routine for your motion devices.
 
Last edited:
Bitmore has a valid point here. Your program shoud have some sort of initiliation routine at startup to correct/reset the positions of your machine.
 
Hmm

Hi guys,

Thanks for the replies so far. The thing is, once the program is downloaded, we have a homing routine that moves the slide back to a homing sensor which then resets everything. As my slide is moving back to the sensor it does it's "funny" movement thing (as mentioned above). Then when it has eventually homed and everything is reset, it continues to do the "funny" movement.

At the moment, I'm not convinced that it is the re-initialisation of the program but I will check it out this morning to rule it out.

Thanks,

Colm
 
Don't forget that the BMOT module is running its own resident motion program which will not be initialised by clearing the PLC memory.

Are you halting this resident program first?

It may be be getting screwed up by suddenly losing its interface to the PLC and only recovering when you reboot it by powering down the backplane.
 
What type of information is being sent over the network connecting your two PLCs? Restarting only one of them with a new program (and wiped data storage) may not automatically refresh the required intialization data.
 
Hi Jim,

The only information being transferred betweent the two PLCs is status information. The information doesn't effect the station where I am seeing my linear slide faults. I have the one of the lines booked for a day next week so I will be able to investigate further, carry out some trials and come up with a reason for my problems (fingers crossed).

Thanks for all the suggestions everybody.

Regards,

Colm
 
I was thinking more about the symtoms, have you changed any velocity or acceleration limits or commands? Could it be that resetting the PLC has also defaulted these limits in the other controller, or has your program changes exceeded these limits already set previously in the other controller?

just a bitmore
 
Last edited:

Similar Topics

Hi, I am trying to get a machine started that was moved from one location to another. It has a Modicon 984-A131 PLC. I have Schneider Electric...
Replies
1
Views
1,013
Dear Friends, I have Schneider PLC which is the world's first one Modicon i need software of Modicon PLC 984,it is known as...
Replies
0
Views
964
I have a Modicon 984 and PLC Workshop for Modicon 32 Bit programming software from FasTrak Software Inc. Is there a way to load the program from...
Replies
6
Views
2,808
Hi all, I have been tasked with a project involving a Modicon E984-275 PLC. I have, unfortunately never used this type of PLC before and would...
Replies
8
Views
3,742
PLC Serial Connectivity Issue with a Modicon 984 and Modsoft 2.21 Hello all from PLCtalk.net, wondering if someone has any words of wisdom to...
Replies
1
Views
5,663
Back
Top Bottom