Hello everyone,

I have a problem with my PF525 overload fault !
It happened to me 3 times in a month !

The motor stopped working and on HMI it showed "motor overload fault" but there is no fault on VFD! it shows everything is normal and I can't reset the fault and start the motor ! I also reboot the PLC and VFD but the alarm was still on HMI! finally I moved the motor by hand accidently and the alarm gone by itself!

any idea if we had an option on PF525 to troubleshoot this problem?

Thanks
 
You need to look at the PLC program - sounds like the PLC program seals on a fault event but doesn't clear it until it sees the motor RPM feedback (?) is greater than zero.
 
As the others have said I would look at the alarm portion of your PLC program. Either the alarm happened and was cleared by the PLC automatically (that's why is it not showing up on the VFD screen) or some other condition caused the alarm to come up. It could be a program bug that is looking at the wrong status bit and is tripping overload alarm erroneously in the PLC/HMI.
You will obviously have to look at the reset portion of the program too.
 
Hello everyone,

I have a problem with my PF525 overload fault !
It happened to me 3 times in a month !

The motor stopped working and on HMI it showed "motor overload fault" but there is no fault on VFD! it shows everything is normal and I can't reset the fault and start the motor ! I also reboot the PLC and VFD but the alarm was still on HMI! finally I moved the motor by hand accidently and the alarm gone by itself!

any idea if we had an option on PF525 to troubleshoot this problem?

Thanks


Check parameters A541 and A542. They might be auto resetting the the drive. As the others have mentioned, the rest of the issue sounds like a programming problem caused by a bit not clearing when the fault goes away.

The other thing I would wonder about is WHY the motor has had 3 over current faults in a month. That seems a little excessive.



Will.
 

Similar Topics

I seem to be on here often lately but cant find specifics about my situation I am trying to control the drive using both ethernet and analog(for...
Replies
1
Views
747
When E300 powered off, the ethernet device tag data stayed at last know state, for example, fault bit is still Off, ready bit is still ON, status...
Replies
8
Views
1,006
Hello all, New to this site - I am adding a new conveyor and using a powerflex 525, though the rest of the drives operating this line are...
Replies
7
Views
1,281
I have a (*) PowerFlex 525 being supplied with 400VAC, 60 cycle, 3-phase. This is not a type-o, this is accurate. Now, the drive clearly states...
Replies
3
Views
1,178
Has anyone had any success using a PanelView Plus to directly control a PF525 over ethernet, I tried to use the file provided with TechNote...
Replies
1
Views
1,059
Back
Top Bottom