how to configure new password on ML 1400 LCD

jugenzhu1963

Member
Join Date
Jun 2006
Location
toronto
Posts
72
Hi

I would like to configure a new password to prevent someone changing the ip address. There is no password at default. Every time i just press the "ok" button to edit the ip address. After i input any number in master password it never accept the new password. How can i setup the new password? i can't find in user manual.

thanks
 
Note: I haven't used passwords on the 1400 but it appears that the Master Password is set using RSLogix500 to edit a program. Under 'Controller Properties' choose the 'Passwords' tab. The program with the new password must be downloaded to the processor.
 
You have to set a password via RSLogix 500 under the Controller Properties on the Passwords tab and download the change to the controller.

For the MicroLogix 1400 there are three available passwords...

Password
Master Password
Subroutine Protection Password

As you can probably see from the LCD it is the Master Password you would need to set to restrict access to changing the IP address.

EDIT: Quick draw Bernie...

Regards,
George
 
Warning !!!
Warning !!

YOU MUST write down the password and have it stored somewhere so that others that do the programming can get to it.

If you are on vacation and the processor dies with no password available, you will get a call to come in and fix it.

You will be required to enter that password everytime you open the program.

james
 

Similar Topics

hi all i am new here i have a mitsubishi smart touch hmi i.e ms-60t-pe but i cannot find a software to edit and download a program in it any help...
Replies
3
Views
153
Hello, I am trying to connect a Stride Analog Output module to a 1769 CompactLogix via Ethernet. I added a new Generic Ethernet Module for the...
Replies
4
Views
225
Dear all, I am beginer in ifix hmi programming. I have 2 ifix 6.0 pc with license FiX and client.. Can some one tell me how to configure sample...
Replies
0
Views
138
Hi all, the machine I am programming the Rockwell PLC for has about 100 parameters that need to be adjusted for every customer. I would like to...
Replies
20
Views
1,937
Within the last week or so, PME has crashed whenever I try to open a configure IO screen. I am running V8.0 Build 6215. Offline configuration of...
Replies
3
Views
384
Back
Top Bottom