Hi guys,
Im trying to make this flowmeter work properly, (Endress+Hauser Promass 83F) i did some batch test to weight my liquid and the totalizer on the promass is prety acturate. its prety much the same weight than the Promass totalizer is reading.
Im using a Metering card 1756-CFM for my contrologix for this flowmeter (input #8 F0 and #10 F0 RET)
On my panelview when i want for exemple, 1000kg i put it in my Target, and when my total reach 1000kg and compare it with my flowmeter totalizer my HMI total is prety much always 4 times higher than the one on my flowmeter...
So if i target 1000kg.... my total on my HMI is 1000kg and my Flowmeter is 250kg
if i put 2000kg for target, the total on my HMI is 2000kg and my flowmeter is 500kg.
We are using a Frequency Output for the mesurement of that promass 83F (Connection #24 and #25)
When im watching my value in logix 5000 it seem that the 2 value im reading is the Netvolume and the Netrate.
I did some simulation test but it look like im not always getting a value, im starting to wonder if my cable and signal is good.... if i get a pulse every 4 pulse or something because my cable is bad it one of the problem im thinking ...
anyway i linked a PDF of my ladder if any of you could look and tell me what test should i try to find my problem or something.
in the Promass83F in the Freq output setting it was:
Standard, passive Positive, Fallback Value, and i should pulse every 2.2046lb.... (1.0 kg)
the min hx is 2.0 and max is 1250hz
Im trying to make this flowmeter work properly, (Endress+Hauser Promass 83F) i did some batch test to weight my liquid and the totalizer on the promass is prety acturate. its prety much the same weight than the Promass totalizer is reading.
Im using a Metering card 1756-CFM for my contrologix for this flowmeter (input #8 F0 and #10 F0 RET)
On my panelview when i want for exemple, 1000kg i put it in my Target, and when my total reach 1000kg and compare it with my flowmeter totalizer my HMI total is prety much always 4 times higher than the one on my flowmeter...
So if i target 1000kg.... my total on my HMI is 1000kg and my Flowmeter is 250kg
if i put 2000kg for target, the total on my HMI is 2000kg and my flowmeter is 500kg.
We are using a Frequency Output for the mesurement of that promass 83F (Connection #24 and #25)
When im watching my value in logix 5000 it seem that the 2 value im reading is the Netvolume and the Netrate.
I did some simulation test but it look like im not always getting a value, im starting to wonder if my cable and signal is good.... if i get a pulse every 4 pulse or something because my cable is bad it one of the problem im thinking ...
anyway i linked a PDF of my ladder if any of you could look and tell me what test should i try to find my problem or something.
in the Promass83F in the Freq output setting it was:
Standard, passive Positive, Fallback Value, and i should pulse every 2.2046lb.... (1.0 kg)
the min hx is 2.0 and max is 1250hz
Last edited: