Scheduling Modules using RSNetworx

Crittenden

Member
Join Date
Mar 2011
Location
Syracuse
Posts
21
I installed AI and AO modules in remote racks and I added Modules to RSlogix 5000 Project online. My question is: I inhibited the modules in project, do I have to uninhibit modules before I schedule Modules using RSnetworx for Controlnet.
 
Welcome to the Forum !

I think that you do have to un-inhibit the modules in the I/O tree before you attempt to schedule the network.

When you schedule a ControlNet network, RSNetworx for ControlNet software interrogates all the connection originators so that it knows how to create the network schedule.

If your connections are inhibited, RSNetworx will probably not place them into the schedule because they won't show up as connection requests from the connection originator (i.e. the ControlLogix).

I can't be absolutely certain about that answer; I've never tried to schedule inhibited connections.
 

Similar Topics

Dear Experts, Thanks in advance for your kind help. I have a GEO SCADA expert 2022 and configure it as a DNP3 master, also I have multiple DNP3...
Replies
0
Views
602
Hi all, New grad working with PLCs for the first time. Today I came across the concept of scheduling when adding new devices to a ControlNet...
Replies
2
Views
1,084
Hi, I am looking at the setting up some new ethernet comms which is originating from an SLC 5/05 to four new identical CompactLogix L24ER's...
Replies
6
Views
2,538
I have a question in regard to taking a ControlLogix L62 PLC (v.16) offline that is currently using controlNet for communications to VFDs etc...
Replies
4
Views
2,539
Dear All, We have redundant system with 1756-L61 with Control net module CNBR/E, Our both Controllers are in healthy state and RM modules are in...
Replies
2
Views
1,382
Back
Top Bottom