Hi all,

Im working on a tank filling project where a pump is started remotely which fills a tank locally.

At the remote location I have a micro820 acting as a remote modbus relay (Slave) to switch on the remote pump.

Its connected via modbus RTU to my local master PLC which is also a micro820.

Master PLC tells the slave PLC to turn the pump on and off, everything is well.

However I have a problem if the following series of events occur:
- Master tells the slave to hold the pump on
- Slave holds the pump contactor on
- There is a connection break in the modbus cable
- Master tells the slave to turn the pump off due to tank being full
- Slave does not receive the message and keeps filling the tank (holds its last value from before the connection broke)

This is a major problem for me if the tanks continue to fill due to a modbus connection break.

So my question is, is there any bit/register/function in connected components workbench which I can use to monitor the status of the modbus link which I can implement to disable the pump output if the slave PLC detects a bad modbus connection?

Cheers
 
I was thinking the same thing as Tarik. A "Heartbeat" would be a good way to go.

One of the simplest Heartbeats is to have a timer in your slave PLC that is reset by the master via Modbus. If the timer is ever done, then you have lost communications and the slave can shut down.
 
Thanks Bullzi

So simple and worked like a charm..

I Put a timer on both ends which are always counting and reset by flashing one shot signals from the opposite ends. If the timers reach 20 Seconds: On the master it brings up a modbus comms error on the HMI and at the slave it blocks the pump from starting until the timers are reset again.
 
Glad it worked!!
I can't take credit for that idea, I got it from another forum member. Just trying to pay it forward.
 

Similar Topics

Title summarizes the overview of the problem. I am trying to make AVEVA Edge 2020 and a Schneider TM241CE40R to talk to each other via Modbus...
Replies
18
Views
1,925
Hello, I need some help/advice. I have a Micrologix 1400 series B on surface at a mine site. Underground I need to read hart data from a flow...
Replies
6
Views
2,213
Hello everyone, M using micrologix 1200 and it is connected to net-aic using pm02 cable, then net-aic is connected to my laptop using pm02 and a...
Replies
15
Views
3,915
I want connect MODBUS RTU device with AB ML1100 PLC to read the holding registers of MODBUS device. In RSLogix 500 I have already configured the...
Replies
13
Views
8,459
Hi, I Have a TSX Premium with ethernet card and a Siemens PLC with a CP343-1 ethernet card. Both can speak Modbus. Anyone who have done this...
Replies
5
Views
5,237
Back
Top Bottom