PV1000 LCD off

edai

Member
Join Date
May 2016
Location
Yogyakarta
Posts
2
Hi all, I have problem that my PV1000 2711-K10G8L1 suddenly LCD screen off. Maybe a backlight is broken. So I check that PV with RSLink on Laptop still can communicate and I upload/back up the program with Panel Builder success.
The situation is I have spare 1 ea PV1000 2711-K10C8 that appear selft test error and cannot appear configuration mode after power up..
I also have 1 ea spare PV1000 2711-K10C1L1 that cannot communicate RSLink on laptop after power up..

Any Suggestion???

Thanks...
 
Welcome to the Forum !

Rockwell Automation Knowledgebase article 69743 (Access Level: Everyone) gives a great deal of detailed information about the interchangeability, repairability, and part numbers for the various backlights used on various PanelView Standard terminals over the years.

By my reading of that document, the backlights in those two PanelView 1000 Color terminals will only be compatible with the PanelView 1000 Grayscale terminal if they are Series F hardware, which uses the same 2711-NL10 backlight assembly.
 
Thank Ken,

Problem solved..
Thats true if the backlight my PV broken different type with my spare.. My solution is I downloaded program to my other unused PV K10G8 and replace the lcd with new K10C1 Lcd cause have same lcd type..
 

Similar Topics

I have a mer or apa file for Pv1000 (2711p-rdt10c) and i need convert this files for Pv5000 (2715P-T15CD-K). Are exist a conversion tool for this...
Replies
1
Views
859
Hi, im looking to migrate a 2711-K10C10 to a 2711P-T12W21 Panelview Plus 7 Standard. I migrate the PV1000 application .pba file in FactoryTalk...
Replies
13
Views
1,949
Hi there everyone! Long time lurker, first time poster. I am doing an SLC-5/03 to CompactLogix migration and am having an issue with a barcode...
Replies
1
Views
1,048
Hi, I'm investigating the feasibility of communication between a old PV standard display and a logix L5X controller via the controller serial...
Replies
3
Views
1,452
Hi all, Anyone manage to get this smorgasbord of hardware to cooperate with each other? PLC - Micrologix 1500 1764-28BXBAA CH1 config - DF1 Full...
Replies
2
Views
1,484
Back
Top Bottom