Issue: Not able to setup produce/consume tags between two controllogix PLC'c on different sub-nets.

Background: PLC 1 is a controllogix running V28, PLC 2 is a controllogix running V24. Since the two PLC's are on different sub-nets, UNICAST settings are applied to the consumed tags on both ends. PLC 2 is working as expected, PLC 1 (V28) is not.

When looking at PLC 1, the producing PLC 1 is flagged with an error - unicast/multicast connection not supported (error code is 16#0108).

"Allow Unicast Consumer Connections " option is selected at both ends.

Question: With the settings the same on both PLC's, the only difference being the controller version - what could be causing this issue?
 
The only time I've ever heard of Unicast support mismatch being version-dependent is if one controller is prior to v16 and doesn't support unicast.

Try power cycling or disconnecting completely. This really does sound like the "Allow Unicast Consumer Connections" feature is not enabled correctly.
 
Please confirm; are these GuardLogix with Safety Partners, or are they ControlLogix Redundancy with two controllers and Redundancy Modules ?

Are the Produced/Consumed tags normal tags or Safety tags ?
 
Plc's are indeed Guardlogix and tags are controller scope safety tags. RPI settings for consumed tags match the safety routine RPI.
 
Just to close up this issue; the problem was a miss-configuration on the producing PLC. The producing tag was not marked to allow unicast connections.

Problem solved.
 

Similar Topics

I have a client who periodically experiences network communication issues. Sometimes when I VPN into the site, their SCADA systems will flash comm...
Replies
2
Views
168
I currently have a setup in Siemens S7 using I-Device connections over PROFINET and I am trying to investigate an equivalent setup using Rockwell...
Replies
7
Views
1,122
Recent Forum member and very-good-question-asker /DesertSurf520 has a thread that started a discussion about Compact 5000 I/O, but branched off...
Replies
11
Views
1,854
My PLC has a Boolean consume tag that gets data from another PLC via ethernet. Is there a way to make the consume tag fail to 0 when the ethernet...
Replies
6
Views
2,751
Hello Ladies and Gents, I have some PLC to PLC communications using Produce and Consume. The data is not time sensitive, and I really only need...
Replies
16
Views
4,649
Back
Top Bottom