1756-L61 communication problems

Crittenden

Member
Join Date
Mar 2011
Location
Syracuse
Posts
21
I have a 1756-L61 controller and since I added modules and scheduled them I've been having problems going online and message reading from other PLC's any answers would be greatly appreciated thanks.
 
What is the communication protocol? ENET, CNET, DNET, etc.

Which of the racks did you add new I/O? Or are all of them new?
 
Well, its getting harder and harder to guess our way to your configuration. Can you upload a running copy, optionally strip out all of programming (be it ladder or ST or FBD) and post the ACD file?
 
Please use complete sentences to communicate with the Forum. It's disrespectful to ask Forum members to guess at your problem and then just give us sentence fragments.

It sounds to me like you've configured the Requested Packet Interval (RPI ) for the analog modules to be so short that the new data is taking up all your network bandwidth.

Did you schedule the network or did you just add the modules to the ControlNet while online ? Online addition of modules on ControlNet means they have to be put into the unscheduled bandwidth of the ControlNet, which could definitely load the network more heavily than you expect.

It's also possible that the way you've programmed MSG instructions is using up more processor connections or buffers than you intend them to.

Posting the *.ACD file would be ideal if you want people to examine your I/O configuration.
 
Sorry I didn't mean to be disrespectful. My company doesn't want me to send the Project for security reasons, but I think you're right Ken about the RPI connections I have them set at 250 ms and the Controlnet modules are set at 250 ms. One AI module is set at 100 ms, I'll set it at 300 ms and the other Modules higher. I'm going to wait till the 5/31 to try it. I will post if it works Thank you.
 
Sounds to me like with all the I/O you have, I would look at setting the RPI's to prime numbers as well so that the PLC is not communicating to all the I/O at the same time, but rather in phases that are appropriate for your process.
 
Hi Mort81 I will change the RPI times differently like 275, 300,325, 500. In the future we are going to split up the ranks and add Processors.
 
Last edited:

Similar Topics

We have Allen Bradley Control Logix 1756-L61B controller with RSLogix5000 v16.03.00 (CPR9) software installed on a reciprocating compressor at a...
Replies
7
Views
16,003
Hi all, Is there anyone having experience on communicate between Allen Bradley Panel View Plus 1500 touch screen and Allen Bradley 1756-L61 PLC...
Replies
18
Views
16,265
Hi All, I'm trying to upgrade from 1756-L61 to 1756-L71 but I keep getting an error 25299-0. Is there anything that need to be complete to be...
Replies
3
Views
1,817
Hi; I am experiencing a problem with AB 1756-L61 controller that it doesn't retain the program while battery is connected. I have found that...
Replies
5
Views
2,759
hello i had a 1756-l61 with firmware ver 13.24. a solid red made the processor not functioning. i ordered a processor that came with firmware ver...
Replies
13
Views
3,802
Back
Top Bottom