The strategy may be simple but I can't figure this out.

Our plant has 8 water cooled chillers and 8 condenser water cooling towers.The condenser water supply temperature setpoint is reset by cascade control based on the average refridgerent diff. pressure of the running chillers.Can anybody please explain how the PLC (AB 5/40E)code may calculate the temperature setpoint based on the chiller refridgerent diff. pressure???


Any suggestions would be really appreciated.
 
I'm assuming that the chillers are using a freon. If they are you will need to find out what type (r-22,r-422, etc).You also need to know various temperatures and the system pressures.


What it comes down to is at certain temperatures/pressures the freon can remove "x" amount of heat, so if the condensor water temp is adjusted for the actual load and other respective temps it would be easier to determine how many chillers to run. I'm not sure on the math and that might vary depending on the type of refrigerant.

If you need more specifics find out more about the system and post that info.

This link might help explain thingshttp://www.chillers.com/RefrigCycle.htm
 
Thermodynamic exchanges are governed by rules and formulas including Pressure, Volume, and Temperature (PV = nRT for pure or perfect gas).

That said, even if it's not a gas, in areas where your refridgerent Volume is read as a fixed parameter, a differential pressure between two points should relate to different temperature values. In your case, I suppose that a diff. pressure indicates the system's ability of temperature absorption (targetted delta_T), useful if a temperature value is given (input or output circuit).

Ask your vendor for the coefficients used in their calculations. You could perhaps approximate the result with some linear function.

Tell us if you find what kind of formula has to be used exactly.

Regards
 
Regardless of the thermodynamics, it sounds to me like what you want to do is create cascaded PID loops. The output of the DP loop is the temperature setpoint for the temperature control loop.
 
hi,
you say the temperature setpoint is reset...
it may be that a minimum differential pressure (0.5 bar )between coolant and product is not being maintained and this is causing the temperature control to shut down.
If this is the case an alarm should be generated by the diff. press monitoring routine.
I doubt if the diff. pressure is used to contribute to the generation of the temperature control setpoint other than to alarm.
 

Similar Topics

Hi I have a scenario where I am controlling ratio of an additive into a uncontrolled Product stream to achieve a certain reading in a pressure...
Replies
0
Views
1,255
I am looking for an example of cascade control with level as the master and floe as the slaver. I am using RSLogix500.
Replies
4
Views
1,636
Hey guys, After spending most of a day Googling looking for the answer, I finally decided to make a thread and ask the experts. I'm trying to...
Replies
5
Views
3,567
RS5000 vs.20, 1769-L35E Processor, I have had an issue that I have seemed to work out between all of the PID posts I could find here and listening...
Replies
0
Views
5,381
Dear all I would like to ask you for help in solving one algorithm, because I never worked with cascade PID. I have to realize heating valve...
Replies
12
Views
8,317
Back
Top Bottom