We're getting the occassional F7 (Motor Overload). error on a PowerFlex 40 drive.
I checked the P033 setting and found that it was set for 9.3 amps. So, while the system was running I watched d003 (Output Current). It stayed between 9.8 amps and 10.8 amps the entire time that I watched it, and up until the F007 fault occurred (after about 8 minutes of run time).
This doesn't make sense to me, because according the manual: "The drive will fault on an F7 Motor Overload if the value of this parameter is exceeded by 150% for 60 seconds."
150% of 9.3 amps is 13.95amps, which I did not observe at any time while the system was running. So, to me, the fault should not be occurring at all. Any ideas?
I checked the P033 setting and found that it was set for 9.3 amps. So, while the system was running I watched d003 (Output Current). It stayed between 9.8 amps and 10.8 amps the entire time that I watched it, and up until the F007 fault occurred (after about 8 minutes of run time).
This doesn't make sense to me, because according the manual: "The drive will fault on an F7 Motor Overload if the value of this parameter is exceeded by 150% for 60 seconds."
150% of 9.3 amps is 13.95amps, which I did not observe at any time while the system was running. So, to me, the fault should not be occurring at all. Any ideas?