Bgardner Member B Join Date May 2016 Location iron mountain Posts 3 Jun 8, 2016 #1 Hoping someone can help I have been trying to connect to a compactlogix PLC and IGS. I can get data for two reads and then I get bad quality and no more reads CIP Error = 0x00 Ext. Error = 00x0000.
Hoping someone can help I have been trying to connect to a compactlogix PLC and IGS. I can get data for two reads and then I get bad quality and no more reads CIP Error = 0x00 Ext. Error = 00x0000.
KalleOlsen Member K Join Date Oct 2008 Location Norway (moustache area) Posts 1,782 Jun 9, 2016 #2 Hi! IGS? Do you mean IGSS from Schneider? Kalle
Bgardner Member OP B Join Date May 2016 Location iron mountain Posts 3 Jun 12, 2016 #3 IGS for GE Ifix 5.5
RussB Lifetime Supporting Member Join Date Oct 2003 Location Michigan Posts 2,914 Jun 12, 2016 #4 As you have an old version of iFix I'm guessing that it did work at one time. What does that error your getting mean it appears rather cryptic?
As you have an old version of iFix I'm guessing that it did work at one time. What does that error your getting mean it appears rather cryptic?
Bgardner Member OP B Join Date May 2016 Location iron mountain Posts 3 Jun 14, 2016 #5 Kepware info says CIP Error 0x0F is Permission denied but it will do two reads when you start up quickclient.
Kepware info says CIP Error 0x0F is Permission denied but it will do two reads when you start up quickclient.
RussB Lifetime Supporting Member Join Date Oct 2003 Location Michigan Posts 2,914 Jun 14, 2016 #6 Bgardner said: Kepware info says CIP Error 0x0F is Permission denied but it will do two reads when you start up quickclient. Click to expand... That may be but you are getting CIP Error 0x00 according to the OP.
Bgardner said: Kepware info says CIP Error 0x0F is Permission denied but it will do two reads when you start up quickclient. Click to expand... That may be but you are getting CIP Error 0x00 according to the OP.
harryting Lifetime Supporting Member H Join Date May 2002 Location Puget Sound Posts 2,595 Jun 14, 2016 #7 What version of Logix ? Newer version allow you to set tag to No Access / Read Only / Read Write. IGS is just rebranded Kepware OPC Server. You can try to set up another channel to the same PLC using default settings and see what happens. Where exactly are you seeing these errors? Is it just limited to certain tags?
What version of Logix ? Newer version allow you to set tag to No Access / Read Only / Read Write. IGS is just rebranded Kepware OPC Server. You can try to set up another channel to the same PLC using default settings and see what happens. Where exactly are you seeing these errors? Is it just limited to certain tags?
taniarox Member T Join Date Oct 2009 Location austin Posts 11 Aug 25, 2017 #8 Did you ever find the solution to this? Having the same issue with IGS 7.5 and CompactLogix L33ER controller. Only 2 reads then nothing.
Did you ever find the solution to this? Having the same issue with IGS 7.5 and CompactLogix L33ER controller. Only 2 reads then nothing.