curlyandshemp
Lifetime Supporting Member
Want to make sure I understand the concepts of introducing VLANs into a control environment. I have inherited a recently installed application where Ethernet time out messages are becoming an issue with EtherNet/IP Powerflex drives.
This application has 6 Compactlogix PLCs, 6 Ethernet/IP Flex IO drops, 30 EtherNet/IP PF523 drives, 2 PV+ HMIs. All devices are on the same subnet and there is another subnet that has an Ignition application with 4 Thin clients.
All 6 PLCs message to each other and all 6 PLCs own at least 1 of the FlexIO drops and at least 1 of the EtherNet/IP PF523 VFDs.
All Ethernet runs in the plant come back to a Stratix 5700 switch in the IT closet. I want to segment this network into at least 2 plant floor level VLANs and keep the SCADA network separate as it is.
Now, if i create 1 VLAN for VFDs & FlexIO and 1 VLAN for PLC to PLC messaging, HMI and programming on the Stratix 5700, does this mean each PLC will need a unique EtherNet communication port to connect to each VLAN?
This application has 6 Compactlogix PLCs, 6 Ethernet/IP Flex IO drops, 30 EtherNet/IP PF523 drives, 2 PV+ HMIs. All devices are on the same subnet and there is another subnet that has an Ignition application with 4 Thin clients.
All 6 PLCs message to each other and all 6 PLCs own at least 1 of the FlexIO drops and at least 1 of the EtherNet/IP PF523 VFDs.
All Ethernet runs in the plant come back to a Stratix 5700 switch in the IT closet. I want to segment this network into at least 2 plant floor level VLANs and keep the SCADA network separate as it is.
Now, if i create 1 VLAN for VFDs & FlexIO and 1 VLAN for PLC to PLC messaging, HMI and programming on the Stratix 5700, does this mean each PLC will need a unique EtherNet communication port to connect to each VLAN?