f2-08ad-1 sensing issues

roni

Member
Join Date
May 2015
Location
INDIA
Posts
37
Hi,
i have resolved all the issues I asked helps. thanks to all.
Kindly reply me, i need to connect 7 inputs to f2-08ad-1, i have wired. (PLC is DL-250-1, module connected to 5th slot) when i use a 4-20 ma injector, none of the values are changing. i wrote the control program as in attachment to load this module. provided various math function to read the values, though nothing happened.
i'm really disappointed, kindly help me out.

Thank you again,
Rons

LOADING.jpg
 
Your setup seems proper for a 5th slot (3rd slot from the right) using BCD and 7 channels.

(Warning, obvious noobie questions) is the PLC in 'Run'? Are you online? (I have had problems - WAY in the past of course - and had found I had done each of these.)

I'll assume you are reading V2000 - V2006 for the resultant values? Could anything else be overwriting these addresses?

For more in-depth help please post a diagram of the wiring. Also zip and post your program.
 
Hi,
thanks for the reply. i'm using v2000-2006, plc in run mode. but, i observed that, the i/o config is not recongnizing this analog module. i got a fatal error of bus failure, then i checked the I/O config and i saw this analog module is missing. when i removed this module, fatal error disappears. i'm suspecting issues with analog module. right na?


thanks,
your reply solved my confusion on setting the slot id and v-memory alocation for analg module. we use only 7 channel, so jumper in +1 must be removed?

Rons
 
Hi Keithkyll,
It has given a separate 24 v dc, confirmed a 23.9V is available in the module. In I/O config, i have tried many kinds of auto and manual configuration, but this module is missing.

what went wrong?

ai new.PNG
 
Last edited:
Hi,
tried different slots, but same result. module also tried with cpu only. lets conclude the error with the module?
 

Similar Topics

I have a pressure transducer: sensotec A = + supply B = - supply C = - output D = + output EXE/SUPPLY 9 - 28 VDC OUTPUT 0 - 5 VDC The analog...
Replies
3
Views
2,413
Pressure Transducer is a FPG2CR,2D5D6A SENSOTEC, Range: 500PSIG Supply: 9 - 28 VDC Output: 0 - 5 VDC A (+) Supply B (-) Supply return C (-)...
Replies
3
Views
1,701
This is a problem that recently arrived on a working machine. I am getting a constant 4095 (12 bit res)in my plc register from my analog card. I...
Replies
1
Views
4,180
Looking for some ideas on sensing contact between 2 metal parts. The application is a part gauge fixture. The gauge and part are both conductive...
Replies
12
Views
2,999
Hello everyone, What's the difference between nominal sensing distance and maximum sensing distance in a diffuse photoelectric sensor ? in...
Replies
1
Views
1,108
Back