ACS850 drive problem

kamrulhaque

Member
Join Date
Jun 2016
Location
assam
Posts
3
I have a ACS 850 drive of 350 KW.It is showing an alarm "PU lost" alarm no. 27 .I am unable to find the reason behind it,as the fault arrised in running condition and the drive is also a year old.
 
0027 PU LOST
(0x5400)
Connection between the JCU
Control Unit and the power unit of the drive is lost.
Check the connections between the JCU Control Unit and the power unit.
 
ACS 850 PU lost problem

I have checked the power supply and OFC cable coming from power supply module to JCU unit its ok.In power cable i am getting 24 V and OFC cable also checked.For confirming that JCU unit has a problem i have replaced a new JCU unit from another VFD odf same rating same problem got transferred in to it and now it is also showing same problem when connected in its original VFD.
 
We were facing the same issue,
After all trials we found the inlet power fuses is blown
And the connection cable between jcu and power unit was not fully plugged.
 

Similar Topics

Hi all, It is my first time using a VFD. The drive is connected to a fan which I need to run at variable speeds - ie. accelerate to a desired RPM...
Replies
8
Views
3,211
I am developing a ControlLogix system. For the VFD I am using an ABB ACS850 VFD. I am planning on controlling the VFD on Ethernet/IP using a...
Replies
0
Views
2,631
Hello, Can the 'X7'port of ABB-ACS850 VFD(Port to connect control panel or PC) be used to connect with PLC system through 'MODBUS TCP/IP'...
Replies
2
Views
2,162
Has anyone had experience interfacing with serial comms a FX3u and ABB ACS850's drives?
Replies
0
Views
2,185
Hello all, I am currently trying to program a PowerFlex 525, version 7.0. We had a power outage recently and when the power was restored, the...
Replies
5
Views
59
Back
Top Bottom