I'm stumped. I have the following Point IO configuration.
1734-AENT Ethernet Module
1734-TBCJC Cold junction Base
1734-IT2I 2Ch Thermocouple input card.
The configuration is functional. I have successfully added it to a L16ER processor, and read data from the module. I can also connect to the internal webserver of the AENT and view the data.
My problem is; when I try to add the Point IO module to the actual machine it will be attached to I am unable to do so. The Machine i'm trying to add it do is a 1756-L61 Control Logix 5561 Controller Rev 20.13.
Initially, I couldn't get either the AENT module or the IT2I module properly configured in the controller tree. The AENT Module Errored with code 16#0203. After some researching I found a post that said to try configuring it with "Connection" in the module definition set to None instead of Rack Optimized. When I tried this, the AENT Module started functioning.
The IT2I card still errors with with code 16#0203 in the control logix processor. The Compact logix processor has no issue with either module even when they are set to Rack Optimized.
Also, the Point IO is on the same subnet as the ControlLogix processor. The Compact Logix is on a different subnet. I would have guessed if I had an issue it would be the other way around.
Any ideas?
Thanks!
1734-AENT Ethernet Module
1734-TBCJC Cold junction Base
1734-IT2I 2Ch Thermocouple input card.
The configuration is functional. I have successfully added it to a L16ER processor, and read data from the module. I can also connect to the internal webserver of the AENT and view the data.
My problem is; when I try to add the Point IO module to the actual machine it will be attached to I am unable to do so. The Machine i'm trying to add it do is a 1756-L61 Control Logix 5561 Controller Rev 20.13.
Initially, I couldn't get either the AENT module or the IT2I module properly configured in the controller tree. The AENT Module Errored with code 16#0203. After some researching I found a post that said to try configuring it with "Connection" in the module definition set to None instead of Rack Optimized. When I tried this, the AENT Module started functioning.
The IT2I card still errors with with code 16#0203 in the control logix processor. The Compact logix processor has no issue with either module even when they are set to Rack Optimized.
Also, the Point IO is on the same subnet as the ControlLogix processor. The Compact Logix is on a different subnet. I would have guessed if I had an issue it would be the other way around.
Any ideas?
Thanks!