I know this isn't the right forum for this but seeing as how you guys seem to know everything. I saw what appeared to be a swing check valve on a main water header with a large hydraulic piston on the bottom and it looks like it is driven from the pump side of the check valve. First time I saw one like it and was curious as to the purpose.
 
Sounds like a check with a "Shock Absorber" for the flapper. This would keep the flapper from slamming open when the pump came on. Must have been a pretty big line.
 
It's probably what's called a Pump Control Valve, used to avoid water hammer. There is a small solenoid valve that controls feed water from the high pressure side (coming from the pump) to a diaphragm connected to a piston like mechanism attached to the valve flapper. So when you turn on the pump, the solenoid closes and the pressure from the pump expands the diaphragm, which slowly forces the flapper open and avoids the surge of water. There is a limit switch on the flapper that only closes when the flapper is fully open, and that limit switch is in the starter hold-in circuit to keep the motor running. A timer in the circuit holds it in until the limit switch activates. If the valve doesn't finish opening before the timer times out, the pump shuts down to avoid cavitation from water not flowing.

When you want to stop the pump, your control system gets the stop command, but the pump stays running and the solenoid for the diagram opens, letting the diaphragm relax and slowly close again, avoiding water hammer. Water hammer is the kinetic energy of the column of moving water getting suddenly trapped and turning into a shock wave because water can't compress. So by slowly closing the valve the energy is dissipated over time and not trapped. Once the valve is fully closed, another limit switch that was holding the starter coil closed will open, dropping out the starter and turning the motor off.
 

Similar Topics

Dear, I am defining a check valve for LPG with Limit switch, is it available in the market? Really appreciate any feedback on this issue. Thank...
Replies
3
Views
1,721
Hey guys, I've recently been asked to review some code at a water treatment plant that isn't working right; seems like sometimes it'll work, but...
Replies
7
Views
5,240
Hello all, I have a Controllogix 1756-L61 with some RIO. There are a couple of 1734-OB4E's that have gone bad. (no output voltage) My boss found...
Replies
10
Views
1,053
Hello I am new here and new to PLC's, I wrote this program for a class that I am taking and my local tech school. The description is switch 7 will...
Replies
0
Views
398
Hello I am new here and new to PLC's, I wrote this program for a class that I am taking and my local tech school. The description is switch 7 will...
Replies
10
Views
1,952
Back
Top Bottom