SIL3 Category 3 application

cocoroco89

Member
Join Date
Mar 2016
Location
Kitchener
Posts
13
Hi,

I am designing safety circuit to meet SIL3 Category 3. Please refer to the attached schematic drawing for detail.
If I connect 7 of gate switches in series, will it still meet Cat 3 requirement?

How many would be the maximum number for gate switches to be connected in series still fulfilling Cat 3 requirement?
 
Last edited:
What type of gate switch are they? Manufacturer / part no.?

If they are mechanical style (eg. tongue and groove) then generally they are not suitable for category 3 and higher applications unless there are TWO gate switches used on the same gate for redundancy.

This is due to the possibility of a single fault preventing the correct operation of the safety system which could be where the screws holding the actuator to the gate fall out and the actuator stays latched into the gate switch.

You can avoid this requirement by using an electronic non-contact style gate switch. Personally I use these as standard in all safety related guarding and haven't used mechanical style switches in a few years. I've can recommend both SICK and Pilz non-contact switches.

As for your question regarding wiring in series, again I can't give an accurate answer without knowing more details regarding the specific type of switch but it is possible to wire certain types in series and still meeting category 3 and higher requirements. For example the two switches I mentioned above have been certified by the manufacturer to be wired in series.
 
Last edited:
What type of gate switch are they? Manufacturer / part no.?

If they are mechanical style (eg. tongue and groove) then generally they are not suitable for category 3 and higher applications unless there are TWO gate switches used on the same gate for redundancy.

This is due to the possibility of a single fault preventing the correct operation of the safety system which could be where the screws holding the actuator to the gate fall out and the actuator stays latched into the gate switch.

You can avoid this requirement by using an electronic non-contact style gate switch. Personally I use these as standard in all safety related guarding and haven't used mechanical style switches in a few years. I've can recommend both SICK and Pilz non-contact switches.

As for your question regarding wiring in series, again I can't give an accurate answer without knowing more details regarding the specific type of switch but it is possible to wire certain types in series and still meeting category 3 and higher requirements. For example the two switches I mentioned above have been certified by the manufacturer to be wired in series.

It is Allen Bradley non-contact switch(440N-Z21W1PH) which comes with dual channel. I confirmed that this switch has been certified to use for Cat 3 or Cat 4. But I am not sure how many would be the maximum to connect in series. Thank you for your feed back.
 
Ahh, yes they are a good style of guard switch to use.

I don't believe there is any limit to how many you can connect in series.

Theoretically it may be possible that you may reach some type of voltage drop or input impedance limit after wiring a HEAP of these in series and depending on total circuit length, but that would be far more than 7.

In my opinion you should be fine.

P.S. Your schematic needs a little work though. Anyone looking at that would assume they are mechanical style guard switches.
 
Ahh, yes they are a good style of guard switch to use.

I don't believe there is any limit to how many you can connect in series.

Theoretically it may be possible that you may reach some type of voltage drop or input impedance limit after wiring a HEAP of these in series and depending on total circuit length, but that would be far more than 7.

In my opinion you should be fine.

P.S. Your schematic needs a little work though. Anyone looking at that would assume they are mechanical style guard switches.

Yes, I confirmed that there is no limitation in connection of this type of switches in series. Thanks for the pointing out the symbol. I will look into the correct ones.
 
Hi Cocoroco89,

That circuit will not achieve SIL 3.
If you give me the part number, DC and PFHd values of your guard switches I can calculate the SIL Level for you
 

Similar Topics

I have an actuator operating a clamp that requires PLd/SIL3, I’ve seen some SMC double valves with feedback, but they are described as dump...
Replies
9
Views
2,331
Can someone please recommend a safety PLC to me, GuardLogix, HIMA, Triconix ..... I have a small program that requires to use 2oo3 voting...
Replies
17
Views
7,590
I've ready through the the previous posts, and we've worked with safety design for a long time. In the past, we worked with Pilz directly, and...
Replies
9
Views
531
Hello Im an Controls Engineer that has been asked to supervise some projects. Im new into this and suddenly everybody is talking about risk...
Replies
1
Views
1,449
I currently design small panels - mostly motor control panels (1, 2, 3 motor) and the owner of the company is asking us to cut back on costs. One...
Replies
6
Views
2,008
Back
Top Bottom