AB Micro 820 with a 2080-MOT-HSC Module.
I have a hall effect flow meter that does 7pulses per gallon.
I have everything working I'm just questioning my math.
I should be able to use GPM = (Pulses per sec * 60)/7 . Is this right or am I missing something?
I know I could simply count the number of pulses in a minute and divide by 7 but that will be to slow of an update as the operator will using this to adjust a valve.

Thanks
 
Your math is correct.
Your accuracy will be based upon the number of pulses per second.
I would find out the longest time you can wait and do the math. If you could wait 5 seconds instead of 1 second you will be more accurate.

Regards,
 
Thanks I will try the 5seconds.
Ultimately I think my issue was the noise filter setting.
I was questioning my math cause I computing 700+ gpm when I should of only been 325gpm. But now with 37 pulses per second and a filter of 10kHz my computed gpm is close to 325.

Thanks
 

Similar Topics

Good day, I have a micro 850 with a 2080-MOT-HSC that is being fed by two flowmeters, Schneider Electric using IMT31's as converters. They are...
Replies
6
Views
421
I'm trying to set up a ring counter - one that transitions from 3599 to 0 (and 0 to 3599 in the reverse direction). My counter insists on...
Replies
2
Views
329
Hello everyone. I'm having some error on the pulses read by the HSC card. I'm using the 2080_MOT-HSC as a pulse counter; in the CCW in using...
Replies
1
Views
601
Hello, So I have a Micro850 PLC with a 2080-MOT-HSC Plug-In module, and i'll be using this for an encoder. I think it was version 11 in CCW...
Replies
2
Views
1,952
MICRO 820 PLC - 2080 MOT HSC - Jencoder J-15S-SL Above plc, add on module and encoder are using to configure one paper cutting machine...The...
Replies
4
Views
3,825
Back
Top Bottom