CLX Output Cards - Commutating voltage

WillM

Member
Join Date
Mar 2015
Location
England
Posts
46
I'm currently going through and integration with an old machine. For the outputs I've spec'd 1756 - OA16's which offer everything I need however there's a part in the manual that's bugging me which I cant find much info on...



Commutating voltage
4V/μs for loads > 50 mA
0.2V/μs for loads < 50 mA(2)

The commutating dv/dt of the output voltage (OUTPUT to L2) should not exceed 0.2V/μs for loads under 50 mA. The commutating dv/dt rating of the module for loads 50…500 mA (OUTPUT to L2) is
4V/μs maximum. If the commutating dv/dt rating of the TRIAC is exceeded, the TRIAC could latch on. If the commutating dv/dt rating is exceeded in the 10…50 mA range, a resistor may be added AC
across the output and L2. The purpose of this resistor is to increase the total output current to 50 mA (I=V/R). At 50 mA and above, the module has a higher commutating dv/dt rating. When adding a
resistor for the output to L2, be sure it is rated for the power that it will dissipate (P=(V**2)/R). If the commutating dv/dt rating is exceeded in the 50…500 mA range, the L1 AC waveform could be at
fault. Be sure the waveform is a good sinusoid, void of any anomalies such as distorted or flattened sections.




I understand roughly what it is saying, that the rate of voltage change can not be at any higher than the values given, however I'm having difficulty getting this info from any of my output devices.


An example of one of the outputs is AB 100-C contactors.
http://literature.rockwellautomation.com/idc/groups/literature/documents/td/100-td013_-en-p.pdf


Any help or experiences regarding this would be appreciated.

Thanks in advance, Will.
 

Similar Topics

Hi all, I cannot find any analog output module for ControlLogix that can output a negative current: -20 mA --> +20 mA ??? Did I miss...
Replies
2
Views
1,663
Controller: 1756-L84E v.35 Prosoft MVI56E-MNETC for ModbusTCP/IP I'm having an issue with some of my write commands. The write command that...
Replies
0
Views
194
I have several Avery scale units and they are configured as Generic Ethernet modules, and I am actually reading the data fine for the weight...
Replies
2
Views
419
What's the best way to move a tag value from the panelview+7 to the clx plc. We display amps from a power meter on the panelview screen, read in...
Replies
1
Views
398
I'm running into an issue migrating a PLC-5 using the newer Logix Designer Export when opening a saved .ACD from RSLogix-5. It has multiple RIO...
Replies
2
Views
616
Back
Top Bottom