Hi, I have SOLA Power Supply SDN 5-24-100p. When I switch it on with load it does not work. If I turn it on without load and after connect ones it works good. Can anybody give some advice? Thanks in advance.
 
Total inrush current is being exceeded or the supply is defective.If it has worked for a reasonable length of time then just replace it. If not or something in the loads have changed, then increase the size to handle the peak inrush current.
 