1734-it2i configuration

xltek

Member
Join Date
Nov 2011
Location
China
Posts
16
I use default parameter value for it2i module configuration and got 260 for room temp. It is ten times real temp, could somebody tell me the way to get correct reading? Thanks
 
The default units are tenths of a degree, Centigrade.

So just divide the integer value by 10.

You can configure the modules for degrees Fahrenheit if you wish.
 