Crimson 3 Gateway Block issues

Bullzi

Lifetime Supporting Member
Join Date
Jun 2012
Location
Colorado
Posts
1,530
Hello Everyone,
I am working on prototyping a blending system. I need to write 6 Real Registers (recipe info) in my L32E out to a Preset Controller via Modbus TCP/IP.

I am using a Red Lion G306 as the Protocol Conversion unit. I have a Gateway Block set up as G3 to Device. The issue is the data doesn't make it out to the device. I am pretty sure that I have the registers correct because if I change it to Device to G3 I get the proper data. See the attached screen shot.

I just wanted to see if anyone had any advice that might help. Since I am am a "one man show" you guys are the only colleagues that I have to bounce ideas off of :)

Let me know what you think.
Thanks!!

G3 TO ACCULOAD GWB.jpg
 
Can you get a mirrored Ethernet port and run Wireshark to see if the data is even attempting to be written to the destination device ?

Or, run ModSim32 on your PC, and substitute your PC's IP address for the Modbus/TCP target device. This can be tricky with firewalls, so disable them for testing.

Have you also tested to be sure the values are being read from the CompactLogix correctly ? If the G3 can't read from the CompactLogix, then there won't be a data change to trigger the Automatic update. Try a timed trigger as well.

ZIP and post the *.CD3 file if you can.
 
Sorry posted the wrong screen shot. Here is the proper one.

Is the Preset Device (ACCULOAD) set up as a Modbus Slave?

Do you have the Ping Register set right on the ACCULOAD Protocol Options? It needs to be a valid 16 bit integer register in the ACCULOAD device. Don't use your real registers.
 
Thanks Guys,
Since the Accuload requires a verification of the the parameters that are changed, it requires a special sequence that must be followed to download to a parameter. So I set it up in a program on the G306 and it is working great. Helps to read the manual. I was only on page 1 :sick:

I have another question about FT View SE Recipe stuff but will post that on a separate post.
 

Similar Topics

Hi, I have to get 5 floating point numbers (Real) out of a CLX L33 Processor via Modbus TCP/IP. I have a Red Lion G09 HMI in the network so I was...
Replies
6
Views
3,549
I'm working with Parker SSD DSI3 which is Crimson 3 in another guise. I've created lots of gateway blocks and as you do attached tags to them. I...
Replies
0
Views
3,565
Hey guys, hoping someone here could give me a little advice. I'm working with a CR1000-04000 in Crimson 3.1 and I was interested in adding the...
Replies
4
Views
97
Hi, I'm having an issue in crimson 3.0 when I create a programme using a case statement referencing a fault word that each bit needs to change the...
Replies
1
Views
83
How do you install update on Red Lion Crimson ver 3.1. Do I just need to run the exe file on the host server?
Replies
1
Views
103
Back
Top Bottom