Slow indicator response PV Plus, Compact Logix

Join Date
Aug 2016
Location
PA
Posts
4
Hello. Working with my first Compact Guard Logix L30ERMS and a PV Plus. I am interfaced to a Fanuc R30iB robot controller through Ethernet I/P.

It seems my indicators have quite a bit of lag to them. I initially started the project with a Proface HMI which I decided not to use for other reasons, but the indicator lag was not there - only with the Panelview

Thanks
 
Welcome to the Forum !

FactoryTalk View does tag reads on a per-Display basis, and the default update time is 1.0 seconds, though in my opinion the roundtrip for Pushbutton -> PLC -> Indicator can look even slower.

You can set this as fast as 50 milliseconds if you have a Display with a lot of pushbutton and indicator elements.

This is one of the weak elements of FTView, and is one of the reasons that the still-evolving PanelView 5550 has a Logix-specific 100-ms pushbutton I/O object.

For ordinary PanelView Plus applications, I generally set the Displays to 250 ms updates.
 

Similar Topics

Anyone have issues with RSLinx being very slow to open. It sometimes will say "Checking Activation" at the bottom for what seems like an...
Replies
2
Views
141
Hi All, we've recently upgraded from FTView SE v10 to v12. Since the upgrade we've been having a problem where the HMI is slow to update tags in...
Replies
0
Views
87
Hi, I have some problem with View Point which I'm using to manual control of conveyors. On begin when in network was only PLC and HMI View Point...
Replies
0
Views
73
Hi. Importing a 2014 aapck in 2023: no problem using it, adding windows, works very well, no problem whatsoever. Creating a new project: as...
Replies
2
Views
748
I am having a weird experience using KepwareEx6 as an OPC Server for a set of SLC processors where the tag data is not updating remotely at the...
Replies
2
Views
568
Back
Top Bottom