question

ioanbz

Member
Join Date
Mar 2015
Location
Bacau
Posts
15
Hi,
the input current recommended is 4-20mA, but I have 34mA.
How can I bring the current parameters required.
Regards,
Ioan

5.jpg
 
Is the 34 mA moving.

Does the 34mA move and it is just high at top end? There should be a zero and span pot on the unit to set min and max output if sensor output moves and is just out of calibration. If this is in a system that has been running the sensor is probaly bad.
 
Has the transmitter ever worked properly or are you trying to get it running the first time?

If it worked before and now outputs 34mA, then it is not regulating the loop current as it should. That's it's job, to regulate the loop current to a maximum of 20mA. If it doesn't do that, there is 99% probability that it is broken and that you need to replace it.

There is 1% probability that a ground loop has been created which adds current to the loop. That could be something like a loop wire with frayed (missing) insulation that touches an ungrounded motor with a winding touching the frame and the differing potentials puts current into the loop. Or water in a junction box, but injection molders typically do not have junction b boxes out in the weather.

The test is to substitute a 4-20mA source (calibrator) and see if the loop current is the same as the calibrator is sourcing.
 
Yes machine worked before, but I had to change the way 1746- NIO4V and then I noticed and value of 34mA.
sensor model is 2200BG C2501A3UA (Gems sensor)
A pressure can lead to 34mA value?
 
Last edited:
The inputs on your card can be configured for voltage or current operation. Have you set the card up properly?

If you disconnect the wires from the card and just connect them to a meter in current measurement mode, what do you read? If this reading is over 20mA then you sensor almost certainly damaged as Dan suggested.
 
It looks like it has 2 outputs connected.
the relais must be in!
btw bad practice to have a 20 mA switched by relais,however it can work.
 
Looks, you have voltages drop, you are not getting 24 volts (Suppose). There is no scaling between 4-34 MA.
 
in the attached image shows a potentiometer (POT 10K).
Can someone tell me what values adjusts the potentiometer?
Regards
 

Similar Topics

I have an HMI 2711R - T4T Series B, and I want to know which PLCs, besides Micro 820, can communicate with it.
Replies
2
Views
61
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
63
I'm working with a project that contains some routines in ST but mostly in ladder. Am I correct in assuming this 'rung': DB1001DO._01AV55_OPEN :=...
Replies
4
Views
100
Is there a way to reset the count on the RS Logix BackUp?? XXXXX PROGRAM IN PROGRESS_BAK445.RSS XXXXX PROGRAM IN PROGRESS_BAK446.RSS XXXXX...
Replies
8
Views
252
I have a few questions about Studio5000. 1. Why is my RA folder so big? its well over 100 GB. 2. How do you delete versions or extra files...
Replies
3
Views
272
Back
Top Bottom