I have an analog input card I am needing to get some 4-20 mA signals off of and I was wondering... in the actual controller tags which ones do I actually use? When I added the card to the backplane a whole list of controller tags showed up for channels faults, module faults, etc... It is in slot 7 of my chassis... do I use the actual Local:7:I.Ch0Data bit and go through the Local:7:I.Ch7Data bit? Im a little confused..
 
If I remember correctly, the contractor who installed it used both methods for various channels, because he could.....

It still causes us headaches, such that any new analogs are specified as Flex I/O and we steer clear of 1756-IF16....
 
It's all in the setup. First off RTFM. That is a MUST with these modules. They can do a lot of stuff. When you first setup the device there are choices... single ended, double ended and high speed, about 9 ways to sunday. These things are great in that you can bring in engineering units instead of just data words. Float, Integers, CST timestamped float or integers... you decide when you setup the card how many channels you will have. AFAIK you can only set these up one way for the entire module.

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1756-um009_-en-p.pdf

you will definitely need the manual.
 

Similar Topics

Hi, I have a ControlLogix system with 1756-IF16 analogue inputs. I can't scale the inputs at the card as there is a requirement to facilitate...
Replies
7
Views
154
Hi all, installed on chassis A17 an A/I from Allen-Bradley , problem is what ever I do , all channels are sticked on value 39.9 and cannot change...
Replies
1
Views
135
Hi Guys, Hoping that someone could please confirm if the 1756-IF16/B is/isn't compatible with the 1756-L1 5550 processor(13.24). I'm sure I...
Replies
2
Views
102
Hello, friends my 1756-if16 differential connection, has been used again (almost 10 years), the measurement value of each channel of the entire...
Replies
4
Views
967
I have an existing 1756-IF16 wired as single ended with all RTNs tied together. Channels 0-3 have 2-wire loop powered devices connected with all...
Replies
3
Views
1,062