I migrated PLC-5 to CLX and for now, we kept the PLC-5 RIO in place. The PLC-5 was upgraded, but the RIO racks were not touched, so nothing would have changed from that aspect. I have a 1771-ASB module for an 8-slot PLC-5 rack. The rack is mixed with IADs and OADs. I can see inputs turning on fine, but when trying to test some outputs, nothing comes alive.
The rack is set for full, and I have no errors.
I migrated PLC-5 to CLX and for now, we kept the PLC-5 RIO in place. The PLC-5 was upgraded, but the RIO racks were not touched, so nothing would have changed from that aspect. I have a 1771-ASB module for an 8-slot PLC-5 rack. The rack is mixed with IADs and OADs. I can see inputs turning on fine, but when trying to test some outputs, nothing comes alive.
The rack is set for full, and I have no errors.