I've hooked up (2) 1000 ohm resistors twisted together in series across the analog input on my PLC to convert the 4-20 mA signal to 0-10VDC. I've confirmed that the two resistors twisted together get close to 500 ohm, I measured with my meter.
The output on my controller to the PLC is scaled appropriately where 0 ft = 4 mA and 10.7' = 20mA.
With a level of 3.12' in the tank I would expect to get 3.12/10.7 = 29% of 10VDC or 2.9V DC. I measure 4.39 VDC and my PLC reads 444.
With a level of 5.24' in the tank I would expect to get 5.24/10.7 = 49% of 10VDC or 4.9 VDC. I physically measure 5.8VDC and the PLC reads close to that at 611.
It appears the PLC is reading accurately, but there is something wrong with the signal being converted by the resistors. Any thoughts?