WinCC – project was developed on PC1 and connection to Simatic PLC was also made there.
The idea is to make a spare Workstation (WS) with the same IP address.

If the main WS (PC1) is broken then I disconnect it off the Ethernet network, connect PC2 and start WinCC RT on PC2.
WinCC project is single-user and has a following feature. WinCC tags are connected to STEP7 with «Named Connection», but not with «TCP/IP» as normally for the single-user WinCC projects.
After starting WinCC RT on PC2 it doesn’t work, cause «Named Connection» is not established, connection driver “is disconnected”, tag values don't transfer from PLC to PC2 and vice versa.
How to set connection between PC2 and PLC ?
 
Last edited:
You need to have simatic net installed and xdb imported and downloaded in station configuration editor.
Also set system parameter for connection in WinCC.
 
Last edited:
Thanks for your reply.

You need to have simatic net installed and xdb imported and downloaded in station configuration editor.

I have “Simatic Net PC Software” on PC2.
Is it sutable as “simatic net installed” ?

May I make on the PC2 the following (instead coping xdb –file from PC1 to PC2) : «Simatic Manager» -- PC Station Folder – right mouse click → PLC → Configure → «Configure» window → clear checkbox in «Use configured computer name» → to put the network PC2 name into “Target Computer» field → press «Configure…» button → «NetPro» -- and I got the message : “PC2 was successfully configured”.
After that I saw 2 new components in «Station Configuration Editor (ONLINE)” window , «Components» tab :
– Index 1 (Application) , “RUN» status ;
– Index 2 (IE General) , “STOP» status ;

I start Index 2 (IE General) component, then it runs for 3 sec., then stops and it’s symbol becomes red again. In diagnostic window I see message “… stopped because PG command”.

But I didn’t connect PC2 to Ethernet Network yet.
Can I be sure if I connect PC2 to Ethernet Network it will work properly ?

How I can now start component 2 (Index 2 (IE General) ) ?


Also set system parameter for connection in WinCC.
Which one ?
 
Last edited:
Right click on Named connections -> System parameter -> Select interface
10848:Simatic_WinCC_rysunek.jpg
 
I can not change the connection channel from «Named Connection» to any other, because PLC is already configured to the IE General (TCP/IP) and I don’t want to reconfigure the PLC HW Configuration, cause it leads PLC to “STOP”.
The main reason of my trouble, I think, is stopped component 2 (Index 2 (IE General) in the «Station Configuration Editor [ONLINE]” window.
 
My “channel” is «Named Connection».
If I open «Named Connection» -- “System Parameter” -- “Unit” Tab , I see

CP-Type/Bus Profile : Named Connection (gray and inactive)
Logical Device Name : VM/ (in dropdown list there is VM/ only)


and nothing there can be changed.
 
WinCC project is single-user. The project is so strange.

I don’t understand why the developer created “Simatic PC Station” object ?

This object is not integrated to the STEP7 completely. In «Simatic Manager» I only can see the “Application” subfolder in the “Simatic PC Station” object folder. There is no OS object inside. There is only HW Configuration.

WinCC project is located in a separate folder on the PC1.

Instead the programmer had to create a simple integrated OS (WinCC object) inside the «Simatic Manager», cause it was the single-user project.

And one more interesting thing. In the «Station Configuration Editor” – “Components_Tab” I see the “Station” as “Operator-HMI”, but in the «Simatic Manager» --- “Simatic PC Station” name shown as “PC_HMI” . There must be the same names !!!

I can’t understand where the “Operator-HMI” name could be taken from ???

But everything on the PC1 works Ok.

I spent almost a week trying to solve the problem.
 

Similar Topics

Hello. does anyone know how I can export my HMI project (in this case an MP277) from SIMATIC manager, so I can open it with WinCC flexible 2008...
Replies
2
Views
6,511
Hello, I am working on a project involving WinCC Flexible 2007 and Simatic STEP 7. The WinCC part is integrated in STEP 7 environment (as...
Replies
9
Views
8,952
I have 2 TIA Wincc projects. One project is in TIA V17 Wincc Professional and other project is in TIA V15 Wincc Advance. How can I copy the Wincc...
Replies
1
Views
1,239
Hi all, I am a bit crazy from behavior of WinCC (actually TIA 15). I have two opened projects and I need to copy some screen items (buttons, ...)...
Replies
3
Views
4,044
Hi! I have no experience at all with VB script but I think I might need something here. The issue is that we mainly have the WinCC Flexible to...
Replies
2
Views
7,335
Back
Top Bottom