Hi Guys;

I have a problem with saving values in Numeric data entry. On every power down; all numeric value lose its value and come back with "0".

I have check everything I can but can't find any setting or anything which lets me to save it. Any help is much appreciated.
 
https://www.rockwellautomation.com/resources/downloads/rockwellautomation/pdf/events/raotm/sessions/manuals/L04-BasicPLCProgramming.pdf

http://literature.rockwellautomation.com/idc/groups/literature/documents/um/2080-um002_-en-e.pdf

'Variable Retention
Micro830 and Micro850 controllers retain all user-created variables after a power cycle, but the variables inside instances of instructions are cleared. For example: A user created variable called My_Timer of Time data type will be retained after a power cycle but the elapsed time (ET) within a user created timer TON instruction will be cleared.
Unlike Micro830/Micro850 controllers, Micro810 and Micro820 controllers can only retain a maximum of 400 bytes of user-created variable values. This means that after a power cycle, global variables are cleared or set to initial value, and only 400 bytes of user-created variable values are retained. Retained variables can be checked at the global variable page.'

Regards,
 
Hi;

Thanks guys for quick reply. I am using PLC 830 and panel view 800. My problem is HMI is showing value "0" for all numerical field after power cycle.

I was talking to rockwell about this issue and they told me that PLC retain all values. As I have shipped plant to site and other engineer is commissioning it; I can't confirm that it does or not so decided to talk with them tomorrow.
 

Similar Topics

Hi! GE proficy numeric data entry animation issue.Im not able to find where i can use tag for visibility.
Replies
1
Views
1,234
I put a Numeric Data Entry Object(NDE) on my screen. Then I made a rectangle(solid pattern). Moved the rectangle over the NDE and set the...
Replies
4
Views
1,578
Hi all so i have a robot project im working on were i need to set the layers. using the hmi screen i would like to use the numeric data display to...
Replies
11
Views
821
Hi everybody, May be a generic question for you advanced programmers, but I do not know how to break it down any further. When any of you are...
Replies
2
Views
1,738
Hi; In numeric input field in Rs View32 works, after writing a value, if we don't press the Enter button from keyboard, value doesn't load. Is...
Replies
4
Views
2,598
Back
Top Bottom