Point io module setup

Join Date
Apr 2002
Location
Just a bit northeast of nowhere
Posts
1,117
Hi all,

Got a point io node, ethernet ip connection is fine. Problem is on the configuration Web page, reports 1 slot. Manually reset to our count + 1, but it reverts to 1 immediately.

Tried to browse chassis, got nothing but module not found, with 11 modules connected.

Must be missing something. Any thoughts?
 
Did you go into the Module Properties for the 1734-AENTR and change the Chassis size? You might have to power cycle the AENTR to get the changes to take place.
 