I have a level transmitter that is going to a P_Ain block and we are alarming the lo and the hi levels. We want the alarm to repeat if the level stays lo for more than 5 mins. How do I do that?


Thanks

James
 
Well you could add an external timer to re-trigger the alarm, but this might add a lot of entries in your HMI alarm log. Or you could edit the AOI with a timer function to do what you want.
 
Well you could add an external timer to re-trigger the alarm, but this might add a lot of entries in your HMI alarm log. Or you could edit the AOI with a timer function to do what you want.

I'm trying to figure out HOW to re-trigger it. I know I need a timer so that when it's in alarm condition the timer starts, when the timer is DN I want to re-trigger the alarm (having more alarm entries is OK). What do I tie the DN bit to in the block to re-trigger the alarm?
 
If it works anything like the ALMA/ALMD you could do an XIO of the external .DN bit on the P_AIn call

Or you could try manipulating the .EnableIn
 

Similar Topics

I need to get rid of this please help When an alarm happen on the HMI it leads to 3 screen popping up and covering all the screen display area...
Replies
3
Views
4,112
Hi All Using RSView SE,can i set the alarm to pop from a certain point of time lest say 7:00 AM to 11:00 PM. Without changing plc code. Thanks
Replies
0
Views
2,099
Hello, I posted a topic on a maintenance alarm system a few months ago which didn't quite work out, but now have a different project with it all...
Replies
2
Views
15,000
Hi, I am looking to migrate some of our Electronic Overloads off of a Troublesome Devicenet Segment. Is there any documentation confirming the...
Replies
5
Views
87
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
Replies
0
Views
87
Back
Top Bottom