Here's a problem I'm sure we've all faced at some point, but I couldn't find an answer when I searched...

You got a +/- 10 VDC signal you want to measure. Your input will only do 0-10 VDC.

My solution is to use a converter to change the negative value to a positive one, and bring the converted value in on a separate input.

Does anybody know of an isolating signal convertor that will change -1 to -10 VDC into +1 to +10 VDC?

Thanks in advance!

TM
 
If you cannot find it make it yourself. Just make simple
voltage divider (two 10k 1% resistors will do):
Connect midpoint of the resistors to your PLC input.
Connect one resistor to your +/-10V analog signal source.
Connect other resistor to +10V.
This will give you output signal 0-10V for input changing
from -10 to +10V.
To make +10VDC source out of 24V just use LM317L and two
resistors. The whole thing costs $3 and ca 10-15minutes
assembly.
 
Last edited:
My original thought was to do it a bit differently, I would have used a full-bridge rectifier. Of course, you would have to compensate for the .7V or so drop across the diodes. You would also have to figure out how to determine the polarity of the original signal, as the new one would always be positive.


The voltage divider solution is probably the better though.
 
Tim,
I have used this device:
MM4380 A
DC INPUT, FIELD RANGEABLE,
ISOLATED TRANSMITTER

You can find them through distributors all over under Wilkerson Instruments. In our area that is PEProducts but you may have a local one to your area.
Check it out. Click on products, then by manufacturer and so on till you get to the page with the spces. If you have difficulty, let me know and I can email them to you.
 

Similar Topics

Does any1 kno how to convert raw/proportional to lbs?
Replies
18
Views
3,665
I have a program that has a scp of 0v to Image dc and in the input minimum it has 1638 and the input max is 14736. The scaled min is 0 and the...
Replies
2
Views
2,170
I am using an analog point I/O input card with a 4-20mA signal. The number comes to an INT tag. I am trying to convert the value to a percent...
Replies
11
Views
3,413
Hello Experts, I am working on S5 to S7 conversion project on which stucked on analog output scaling. In S5 following logic is written for...
Replies
5
Views
3,021
New to programming, please excuse what I'm sure is a long and stupid question: I'm building a training workstation with a CompactLogix. I have an...
Replies
12
Views
2,811
Back
Top Bottom