Hi all
I found this Shortcut {::[SLC500]B18:10,L2} in a PV+ pointing to an SLC500. Is it 32 bit looking at B18:10 + 11?
Only 16 bits (B18:10) are used in the PLC & HMI program.

Now for the stupid question. would L3 = 48 bit & L4 = 64 bit?

Cheers
Ian
 
Okay found this in Document 25342 on Rockwells site.
The L2 value is the array size and can be up to 10 (L10) for 10 consecutive Bit registers but can be bigger for N registers.
Probably the reason I did not recognise it is it only (?) applies to HMI alarms, something I have not dealt with a lot.
ian
 
You've got it; that's a typical address for a two-Word block of data used for Alarm triggering in a PanelView Plus.

The thing that I always have to get straight is that when you use "Least Significant Bit" (LSB) mode for triggering Alarms, Bit 0 of the Word is Alarm trigger position 1.

I've done a lot of applications for PV+ where the first test showed "hey, the wrong alarm is showing" because I forgot that difference in numbering.
 

Similar Topics

I have no experience with Eaton HMIs. I downloaded the Galileo software and I am trying to get the file on a HMI (XV-102-H3-70twrl-10) to modify a...
Replies
3
Views
36
Sorry for my lack of knowledge, beginner here. Yesterday, we had a Pro-Face SP5000 HMI fail on us. The technician said that the HMI had the blue...
Replies
0
Views
33
I have an HMI 2711R - T4T Series B, and I want to know which PLCs, besides Micro 820, can communicate with it.
Replies
2
Views
53
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
8
Views
121
Hi, Wy we log data in PLC using DLG instruction, when we have option to log data in HMI
Replies
1
Views
70
Back
Top Bottom