Anyone know why the resolution for a display on a 15 inch PVP7 (V8) standard is 1018 x 762?? when you select the HMI type it has 1024x768.

It's not a big deal but when I load a MER I can actually see the wasted pixels and my display is not even in the center of my screen. Surely it's just a setting or something but I can't find anyone else posting about it.
 
Where are you seeing the six-pixel discrepancy in software ?

Is the display justified to the upper left corner ?

I have one of these in assembly right now and haven't seen the same symptoms, but I created the project by opening an old PV+ 5.10 application as the base project for my new machine HMI.
 
After I posted this I did look at an earlier project with the same screen model and it had 1024x764 (Edit: This value I am getting from the display settings and it is set to "replace" not "on top".) I think It potentially could be because I started the project from a PVP Non-touch old school screen from back in the day.

All my objects which are justified to the left are set at position 0 and when I test application it looks good, it's only when I download it to the panelview where I see my displays don't go all the way to the ends of the screen.

My last resort might be to start a project from scratch and copy past all my content.
 
In the Project Settings:

I get 1018 x 739 when I specify that I want a title bar for the project.
I get 1018 x 762 when I specify no title, but with a border.
I get 1024 x 768 when I deselect both border and title.

OG
 
In the Project Settings:

I get 1018 x 739 when I specify that I want a title bar for the project.
I get 1018 x 762 when I specify no title, but with a border.
I get 1024 x 768 when I deselect both border and title.

OG

This was it, border was ticked. Must have been from the previous project. After all these years of using FT I still find things I've never used.
 

Similar Topics

Duplicated a Panelview Plus 7 15",to a Panelview Plus 10"and resolution is messed Up Good Afternoon , I just finished a Panelview Plus 7...
Replies
0
Views
1,193
I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
78
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
53
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
Replies
3
Views
77
Hello everyone. This is more of an HMI issue. I have a new PanelView Plus 7 Series B. I am using the alarm list object to display the fault...
Replies
0
Views
89
Back
Top Bottom