1769-L32E REV20.12

I have had a customer PLC loose the date twice now on the same PLC. I ask if there have been any power outages and they say no.

Every time I go in to check the date/time it shows ??
If I look at wallclock year it shows 1969.
it has happened 4 months apart. month and day went to 4/22.

The PLC does not stop in operation but some numbers I am recording using hour/day/month get screwed up.

Anyone else see this behavior? o_O
 
Check for SSV instructions and see if any are addressing the WALLCLOCK object. That way you can identify if anything in the logic is changing the time.

You might look at programming something to capture power cycles. Just in case they aren't catching power blips. You could do something simple like a XIC bit using S:FS and triggering a counter.

OG
 

Similar Topics

I just found two old 1769-L32E controllers in the plant that I cannot go online with using my version of Studio 5000 (30.14). I've reached out to...
Replies
5
Views
1,953
Has anyone experienced the following issue on RSLogix5000 (currently on V16) I have a PLC program that has been running on a site for a number...
Replies
5
Views
1,595
Hello; We have an Allen Bradley compact logic processor at an auto glue kitchen of corrugator machine which connected with AB HMI. Normally to...
Replies
5
Views
2,424
Hello all, I have a small issue that I'm sure is something I overlooked but I'm stumped so I'm hitting the old Interweb to ask for help. On my...
Replies
11
Views
3,943
Using Rslogix 5000 Data Access manual as a reference I keep getting 'Service Not Supported' response when using symbol instance addressing to...
Replies
2
Views
1,552
Back
Top Bottom